#7146 - 01/24/02 01:23 PM sub panel feeder wire sizes......
duanet Offline
Junior Member
Registered: 12/02/01
Posts: 5
Hi,
I am installing a new 125 Amp sub panel 65 feet away from a new 200 amp service. The sub is located in the same shop as the main panel. Do i need to pull a separate grounding conductor for the sub or can the EMT between the main and the sub be used for the grounding bond? I ask as i would like to use 1-1/4 EMT which will only allow three #1 copper conductors.
(per conduit fill table 3B)
Thus allowing 2-#1 lines and a common max.
If i have to pull a separate #6 ground i would have to step up to the 1-1/2 EMT. Basically i wish to know if on a sub panel situation such as this is it allowed to use the EMT conduit as the ground rather than a separate conductor?

thanks
Top
Work Gear for Electricians and the Trades
#7147 - 01/24/02 02:22 PM Re: sub panel feeder wire sizes......
dana1028 Offline
Member
Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
I'm now looking at Appendix C of the 1999 NEC, pg. 585 - THHN #1...4 conductors (#1 size) are allowed in 1-1/4" EMT
Top
#7148 - 01/24/02 02:28 PM Re: sub panel feeder wire sizes......
duanet Offline
Junior Member
Registered: 12/02/01
Posts: 5
You may want to check again as my NEC book Table 3B (maximum # of conductors in trade sizes of conduit or tubing) states that a maximum of 3 #1 THHN in 1-1/4
Top
#7149 - 01/24/02 02:48 PM Re: sub panel feeder wire sizes......
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Where the heck is table 3B?

Table C1 on page 585 is the correct one to use & as dana1028 pointed out 1 1/4" emt is good for 4 #1's.

You don't usually need to pull in the equipment ground, but many electricians prefer to include one in all their conduit work.
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#7150 - 01/24/02 02:51 PM Re: sub panel feeder wire sizes......
duanet Offline
Junior Member
Registered: 12/02/01
Posts: 5
Table 3B is in chapter 9 (tables and examples) page 750 of 1990 NEC
Top
#7151 - 01/24/02 05:54 PM Re: sub panel feeder wire sizes......
Anonymous
Unregistered

duanet,

Its time to invest in a new NEC book.
Top
#7152 - 01/24/02 07:37 PM Re: sub panel feeder wire sizes......
eman1963 Offline
Member
Registered: 01/24/02
Posts: 22
Loc: rhode island
i would use the 1 1/4 emt as the ground and run only 3 conductors
Top
#7153 - 01/24/02 07:38 PM Re: sub panel feeder wire sizes......
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
What size breaker are you installing ?
Top
#7154 - 01/25/02 03:56 PM Re: sub panel feeder wire sizes......
dana1028 Offline
Member
Registered: 01/09/02
Posts: 163
Loc: San Carlos, CA
BTW - Appendix C, pg. 585 does say 4 #1 are allowed in 1-1/4" EMT; however if you do the arithmetic from Table 4 & Table 5 (EMT usable space & area of THHN tables)you cannot use 4 #1s in 1-1/4" EMT.

However, even though you are allowed to use the EMT as the EGC, I highly recommend you do pull the #6 (the arithmetic works) as your EGC - don't trust the EMT connection over the years to be maintained and work when needed in the event of a fault.
Top
#7155 - 02/05/02 08:03 PM Re: sub panel feeder wire sizes......
3rd degree Burns Offline
Member
Registered: 02/04/02
Posts: 36
Loc: Dallas, Texas, USA
I have to agree with Dana, don't trust conduits to carry the ground as the years progress...I've already seen far too many lost grounds from installations 15 to 30 years old. Go ahead and pull it, you won't regret it later.
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 35 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals