#71141 - 10/23/06 03:20 PM Multi-wire branch circuit voltage readings
poorboy Offline
Member
Registered: 06/02/05
Posts: 124
Loc: Central Maine
New install in a retail store. Adjacent receptacles in a telcom room on a 12/3 MC homerun. If nothing is plugged in, you have 120 V to neutral on each circuit. If you plug in a security system transformer you have 200+ volts to neutral on the other circuit(which still has nothing plugged into it). If I unplug that and plug my 3 prong tester into the circuit I Read 176 volts to neutral on the other circuit. The condition came to light when the inspector plugged his 3 prong tester in to the second circuit with the transformer plugged into the first and saw two green lights and an orange. What am I missing here? Checked the wiring and found no problem---ckts are on different phases and share a neutral. 120 volts is derived from a transformer since this is a 480/277 service.
Top
Work Gear for Electricians and the Trades
#71142 - 10/23/06 03:25 PM Re: Multi-wire branch circuit voltage readings
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
It really appears the neutral is not correctly wired.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#71143 - 10/23/06 03:57 PM Re: Multi-wire branch circuit voltage readings
JoeTestingEngr Offline
Member
Registered: 11/04/05
Posts: 781
Loc: Chicago, Il.
I sure hope that your Neutral is coming from the bonded secondary center tap of that transformer.
Joe
Top
#71144 - 10/23/06 04:04 PM Re: Multi-wire branch circuit voltage readings
Zapped Offline
Member
Registered: 10/01/02
Posts: 482
Loc: Huntington Beach, CA, USA
I've seen very similar readings from loose or mis-wired neutrals also. That would be my first guess. Please let us know what you find out...
Top
#71145 - 10/24/06 01:21 PM Re: Multi-wire branch circuit voltage readings
poorboy Offline
Member
Registered: 06/02/05
Posts: 124
Loc: Central Maine
Went back and looked in the panel today. The guy who made it up had the neutral from the 12/3 spliced to a piece of white THHN because it would not quite reach the neutral strip on the bottom of the panel. I followed this THHN down, across the bottom of the panel, past the neutral strip, back up the other side of the panel where it was wirenutted to the neutral tail from a GFCI breaker. Apparantly he had intended to use this piece of THHN to lengthen both neutrals so they would reach the strip. All he forgot was to CUT IT IN THE MIDDLE AND ATTACH EACH ONE TO THE NEUTRAL STRIP!!! Keep your eye on your help and never assume anything.

[This message has been edited by poorboy (edited 10-24-2006).]
Top
#71146 - 10/24/06 01:37 PM Re: Multi-wire branch circuit voltage readings
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
LOL!!!! I shouldn't laugh, though, sounds like something I'd do!
Top
#71147 - 10/25/06 05:56 AM Re: Multi-wire branch circuit voltage readings
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
It's amazing how much better something works if it's wired up correctly!
Top
#71148 - 10/25/06 06:15 AM Re: Multi-wire branch circuit voltage readings
Zapped Offline
Member
Registered: 10/01/02
Posts: 482
Loc: Huntington Beach, CA, USA
Thanks for the update poorboy. I'll keep that information in my troubleshooting brain-file...
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 40 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals