The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 102 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#69498 - 09/11/06 10:40 AM Grounding at Panel...
Cinner Offline
Member

Registered: 12/01/04
Posts: 77
Loc: Kelowna, B.C., Canada
When the power authority company brings you the cables for a residence, they bring 2 hots and a white...is the white wire grouded back from where it is fed or is it just the center point of a transformer...I was thinking of the possibilty of grounding the wire twice and the causes of that...circulating currents?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#69499 - 09/11/06 12:21 PM Re: Grounding at Panel...
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Yes the PoCo does ground the neutral.
There are parallel currents all over the place on the line side of the service disconnect and the NEC is silent on it. That is NESCland and they don't care.
I can see about an amp of "neutral" current on my ground electrode conductor and a similar amount on the ground wire going up the pole outside.
_________________________
Greg Fretwell

Top
#69500 - 09/12/06 03:05 AM Re: Grounding at Panel...
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
We have several different grounding arrangements here, but the the neutral is always grounded at source by the power company.

Our PME / TN-C-S system is the most like standard American practice, and has the neutral re-grounded locally at the service entrance, so we can have parallel neutral paths line-side of the meter too.