#69372 - 09/06/06 05:15 PM underground service and meter
velect Offline
Member
Registered: 05/01/04
Posts: 81
Loc: st joseph mi usa
I have installed a meter 200 feet away from the building with the only disconnect being in the building at the point of entry. Inspector says I need a disconnect close to the meter. I think he is wrong
Top
Work Gear for Electricians and the Trades
#69373 - 09/06/06 05:27 PM Re: underground service and meter
LK Offline
Member
Registered: 01/21/03
Posts: 1429
Loc: New Jersey
"I have installed a meter 200 feet away from the building"

200ft away from the building being served?

More information please, what did your utility say about this installation?

And when you applied for the permit, did you include a plan with the intended layout with your permit application?
Top
#69374 - 09/06/06 05:31 PM Re: underground service and meter
yanici Offline
Member
Registered: 09/03/06
Posts: 58
Loc: Atlantis
230.70(A)(1) "The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of enterance of the service conductors."

If your meter is remote, then I believe you'll need the service disconnect remote also. You can pedestal equipment that will hold your meter and main disconnect in one unit.

Why does the meter have to be 200 feet away anyway? If you move it to the building you'd ba OK.
Top
#69375 - 09/06/06 05:45 PM Re: underground service and meter
velect Offline
Member
Registered: 05/01/04
Posts: 81
Loc: st joseph mi usa
Plan reviews are not required in Michigan unless the Service is 400 amps or more....or the building is over 3500 sq feet.

The POCO would not run overhead or undeground through the woods.......so we trenched it in ourselves

[This message has been edited by velect (edited 09-06-2006).]
Top
#69376 - 09/06/06 05:51 PM Re: underground service and meter
yanici Offline
Member
Registered: 09/03/06
Posts: 58
Loc: Atlantis
Since you own the lateral and not the POCO, it looks more and more like the AHJ has you.
Top
#69377 - 09/06/06 05:56 PM Re: underground service and meter
velect Offline
Member
Registered: 05/01/04
Posts: 81
Loc: st joseph mi usa
I have put services in before that the meter was on one side of the house and we buried the conductors over to the other side of the house at the point of entry with only a disconnect on the main panel inside with no issues from the inspector. Granted it wasn't 200 feet but I see no difference
Top
#69378 - 09/06/06 05:59 PM Re: underground service and meter
yanici Offline
Member
Registered: 09/03/06
Posts: 58
Loc: Atlantis
Yeah, I know what you mean. These guys change their minds like the weather sometimes. What you want seems safe enough, but they wear the badge.
Top
#69379 - 09/07/06 05:19 AM Re: underground service and meter
XtheEdgeX Offline
Member
Registered: 04/17/05
Posts: 116
Loc: Florida
A friend of mine recently did a similar installation. The house was several hundred feet away from the street. He installed a shunt trip breaker for the main. He installed a pushbutton at the street by the meter, so the main could be opened there, as well as being able to manually open it at the house.
Top
#69380 - 09/07/06 09:00 AM Re: underground service and meter
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I am not sure what the inspector is citing as a code reason for his ruling. Is there some local code? In fact the NEC would allow a single disconnect, either immediately where it enters the house, out there at the meter or anywhere in between. Perhaps a bad design but not illegal.
At a certain point you still have to work there so it may be easier to just ask what he wants.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 59 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals