#69138 - 08/29/06 04:01 PM Lathe motor
derater Offline
Member
Registered: 03/30/02
Posts: 179
Hope this is an ok area for the ?. Cust. has a Powermatic 3520b lathe and all I can find is that it's 3 or single phase, 2hp. Someone (co. ?) told him it takes a 40a breaker. Does this seem excessive? Resi basement location.
Top
Work Gear for Electricians and the Trades
#69139 - 08/29/06 04:38 PM Re: Lathe motor
Bob Offline
Member
Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
Look on the motor nameplate and get the FLA
(full load amps). If its single phase the FLA should be about 12 amps. Use a 25 or 30 amp breaker. If its 3 phase the FLA should
be about 7 amps. 15 or 20 amps breaker. usually a residence does not have 3 phase service. You may have to change the motor.
Top
#69140 - 08/29/06 04:57 PM Re: Lathe motor
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Don't be too quick to jump to the conclusion that it's a 230 volt wired motor.
A 2hp motor will draw about 24 amps when wired for 115.
If that were the case, a 40A Breaker wouldn't be excessive
Top
#69141 - 08/29/06 05:11 PM Re: Lathe motor
LarryC Offline
Member
Registered: 07/05/04
Posts: 780
Loc: Winchester, NH, US
If it a 3 phase motor, you can use a small VFD to generate the 3 phase from a single phase input.

Larry
Top
#69142 - 08/29/06 05:47 PM Re: Lathe motor
derater Offline
Member
Registered: 03/30/02
Posts: 179
Thanks guys. It's an either/or unit. I don't carry 8-2 in the van and was hoping against another trip for wire. Electure, is that run or start? Does that apply?
Top
#69143 - 08/30/06 08:09 PM Re: Lathe motor
RobbieD Offline
Member
Registered: 02/23/03
Posts: 231
Loc: Canada
Here is the link with the manual for the lathe. It seems wierd that in the specs it doesn't list the FLC. It does state that it is a 230v motor like you said single/or three phase.

http://www.wmhtoolgroup.com/shop/index.cfm?navPage=4&iid=6056397
Top
#69144 - 08/30/06 09:13 PM Re: Lathe motor
NORCAL Offline
Member
Registered: 09/25/02
Posts: 865
Go to page 13 of the manual, it already has a inverter.
Top
#69145 - 08/30/06 09:32 PM Re: Lathe motor
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
Viewed the .PDF manual, available from the link that RobbieD provided.

Found out the following about this Lathe:

<OL TYPE=1>

[*] The Lathe Motor is powered and controlled via an intregal VFD, which is Factory installed,


[*] The Motor is a TEFC make, rated for 2 HP at 220V, 60 Hz,


[*] No indication if the 2 HP Motor is Single Phase or Polyphase - but seeing that the Motor is controlled by a VFD, I am thinking it would be a Polyphase Motor - likely a Wye connected TEFC type 3 Phase Squirrel Cage Induction Motor,


[*] The machine may be connected to either a 1 Phase 230 Volt power system, or a 3 Phase 230 Volt system,


[*] If 1 Phase 230 Volt, 2 Wire system is used, the Factory's Standard 3 wire cord, supplied with the machine, may be used and no alterations need to be made to the machine,


[*] If 3 Phase 230 Volt 3 Wire system is used, the cord needs to be changed out with a 12/4 cord, and termination alterations are required.
</OL>

No FLA ratings are listed anywhere, so it seems like the Branch Circuit might be best rated for the FLA of a 2 HP 230 Volt 1 Phase Squirrel Cage Induction Motor.

As viewed by the NEC, this would result in at least 12 FLA for a 230 Volt Motor, and at least 13.2 FLA for a 208 Volt Motor.

Looks like a 20 Amp Circuit would be sufficient for the Lathe, and a Breaker from 20 Amps to 40 Amps could be used.

Definitely need to do these two things first:

1: Check the nameplate's ratings, and base circuitry ratings from that,
&
2: RTFM!!!
(stands for: Read The Fu..,, err... Fine Manual)

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#69146 - 09/01/06 04:32 AM Re: Lathe motor
derater Offline
Member
Registered: 03/30/02
Posts: 179
Thanks all- I finally got to see the lathe; nameplate read 17.5a @ 240v 1ph.Used 10-2 for the circuit,20a bkr. Why 'they' told the h/o 40a is beyond me.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 36 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals