#69129 - 08/29/06 04:09 AM feeder protection
carranoelectric Offline
Junior Member
Registered: 08/28/06
Posts: 4
Loc: stratford ct
Is the secondary feeder from a 75 kva xfrm protected from the primary breaker? I have a 100 amp 480 v breaker on the primary with a 200 amp 208 v secodary to a panel. Do I need a 200 amp main or can I use main lug and have the 100 amp breaker protect the 200 amp feeder?

[This message has been edited by carranoelectric (edited 08-29-2006).]
Top
Work Gear for Electricians and the Trades
#69130 - 08/29/06 04:27 AM Re: feeder protection
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
NEC 2002 240.21(C)(1) says you need a breaker on the secondary within a limited distance.
_________________________
Ron
Top