#6889 - 01/12/02 09:53 PM can lights in soffit
amp-man Offline
Member
Registered: 06/23/01
Posts: 141
Loc: Sacto, California US of A
Hi y'all,

Need your opinions on this--

Adding two mini (4") can lights in a kitchen remodel. Soffit into which they are going encloses a space 8' by 1' by 6".

The cans are Halos, non-IC. Lamps are 40W mini reflectors (tungsten). Can instructions call for 3" clearance from combustable surfaces. Plenty of clearance except on top, where there is about 1" clearance above the housing.

The top of the soffit is a conventional drywall ceiling (the ceiling is finished, so the soffit must be part of a remodel).

Questions:

1. Am I O.K. with less than 3" clearance above? I think so, because the surface above, being finished drywall, is considered non-combustable.

2. The soffit is essentially unventilated. It encloses a pretty good volume (~4 cubic feet). Should I be concerned about heat buildup, and if so, would providing a few 1/2" holes above each housing be a good idea?

Thanks in advance--

Cliff
Top
Work Gear for Electricians and the Trades
#6890 - 01/13/02 05:13 AM Re: can lights in soffit
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
I believe you would not have a problem with the lamps you are using. The problem may come if someone at some point throws some higher wattage or halogen lamps in. Some ventilation may not be a bad idea. Can you possibly cut out the drywall above the light?
Top
#6891 - 01/13/02 12:39 PM Re: can lights in soffit
Sandro Offline
Member
Registered: 12/30/01
Posts: 444
Loc: Stoney Creek, ON, Canada
I believe the built-in thermal overload would kick in if a higher than rated wattage bulb was put in.
Top
#6892 - 01/13/02 02:00 PM Re: can lights in soffit
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
I do agree that the overload should protect from any fire issues. What I would be concerned with if somebody were to install a higher wattage lamp, and then the light starts to go off and on....."What did that electrician do?" YOU look like the dummy!
Top
#6893 - 01/13/02 02:24 PM Re: can lights in soffit
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
amp-man

You shouldn't have any problems with clearance above, as standard cans are engineered with only 1/2" space left above them to a wood floor above. I mean that the standard height can is 7 1/2" high which only gives you 1/2 inch (at best) above in a 2 x 8 ceiling. Same with shallow cans (5 1/2" in a 2 x 6 ceiling)

Some ventilation holes sound like a good idea.

Bill
Top
#6894 - 01/13/02 05:26 PM Re: can lights in soffit
amp-man Offline
Member
Registered: 06/23/01
Posts: 141
Loc: Sacto, California US of A
Scott, Bill, Sandro--

Thanks for replying.

Think I'll put 'em in and leave it at that. Bill's point about the intended clearance, given the height of the can and the joist height, is convincing.

If I ever get a report of blinking lights, then I'll put some ventilation holes in...and I'll come back tell you about it, and Scott can say, "I told you so..."!
Top
#6895 - 01/13/02 05:31 PM Re: can lights in soffit
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
I will be waiting!
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals