#68828 - 08/17/06 12:27 PM Welding on conduits
Amazingmg Offline
Member
Registered: 05/04/05
Posts: 42
Loc: Florida, USA
An engineer wants us to weld 4" conduit nipples to a bulkhead plate for exiting a freezer building. The plate would intersect the nipples halfway....so half the nipple sticks outside...half inside.

Welding on conduits (even while no wire inside) just seems wrong, but I'm not sure there is no reason we can't do this.

Any thoughts?
Top
Work Gear for Electricians and the Trades
#68829 - 08/17/06 12:57 PM Re: Welding on conduits
macmikeman Offline
Member
Registered: 07/16/02
Posts: 717
Loc: Honolulu, Hawaii
Try looking at 300.18(B) and see if that helps at all.
Top
#68830 - 08/17/06 01:06 PM Re: Welding on conduits
Tiger Offline
Member
Registered: 05/04/05
Posts: 706
Loc: Crystal Lake, IL USA
Also welding galvanized steel creates a poisonous white cloud of zinc oxide, I believe.

Dave
Top
#68831 - 08/17/06 01:22 PM Re: Welding on conduits
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
It always looked yellow to me but you better be wearing a respirator anyway.
300.18(B) is the real answer. Good call Mike
_________________________
Greg Fretwell
Top
#68832 - 08/17/06 02:37 PM Re: Welding on conduits
hypress Offline
Member
Registered: 07/20/04
Posts: 129
Loc: Charleston WV
What would be wrong with a "Myers " bulkhead fitting. Time you figure your welders time it might be cheaper to use bulkhead fittings.
Top
#68833 - 08/19/06 11:28 AM Re: Welding on conduits
Amazingmg Offline
Member
Registered: 05/04/05
Posts: 42
Loc: Florida, USA
300.18 (B)

Aha! Sometimes these guys direct us to do some of the screwiest things...so basic that it seems hard to immediately answer why it is wrong.

On the gas...we do weld HDG brackets all the time (outside) so I knew about that. Good comment though.

What I proposed to the Eng. was nipples thru the wall (wall is 6" thick with ins. core and galv. skin) with O-Z Gedney CDS? sealing bushings (the feeder is 3-500mcm per phase in tray up to wall on either side). Then have mechanical guys flange/seal around conduits as they see fit (I think we can get them pretty tight). They are worried about thermal loss. This is a cold storage building. Or a EYD with Chico on either side.

Thanks for help. I haven't even had time to break open the code book till just now. Crazy lately...working 6-7 days most weeks. Wife is real happy....<sarcasm>
Top
#68834 - 08/20/06 09:46 AM Re: Welding on conduits
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Possible solution is to weld a metal sleeve in the bulkhead and use a Link Seal between the sleeve and the conduit.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#68835 - 08/20/06 11:51 AM Re: Welding on conduits
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
In naval use, we weld steel stuffing tubes and swage tubes to bulkheads all the time. Provides a full watertight and mechanical seal. And if used with a grounding adapter, provides full EMI/EMP protection, too. They all come with threads for attaching conduit adapters and anything else you might need. This might be an option too, if your engineer insists upon welding!
Top
#68836 - 08/21/06 07:29 PM Re: Welding on conduits
Active 1 Offline
Member
Registered: 02/22/03
Posts: 687
Loc: Grayslake IL, USA
I just signed up for an auto welding class to help with my hobbies. Anyway I seen in the textbook you can weld galvenized steel (without grinding it off) but it looked much more difficult to get a good weld for many reasons. The big tip was you got to crank the welder setting higher than normal.
Top
#68837 - 08/23/06 12:11 AM Re: Welding on conduits
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Isnt metal also thermally conductive as well as electricaly? Sounds like some sort of sleeve like iwire posted would be better for the purpose. Even a big gapping hole and a can of foam would be better IMO.

Also heres an interesting code and kinda funny when you see why its there, or not too funny depending on the situation. 300.7

Funny one: Jelly jar light filled with water.

Not funny: Rotted out disconnect falls apart when the AC mech LOTO's his switch, and and finds that it only partialy opens as it falls apart inside from rust.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 47 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals