The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
Yesterday at 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 6
renosteinke 6
ghost307 5
sparky 4
Who's Online
1 registered (Radar), 321 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#68803 - 08/16/06 05:39 PM Shunt trip breakers
Peter Offline

Registered: 06/08/04
Posts: 93
Loc: San Diego
I was hooking up an Ansul system today with a shunt trip breaker. I connected the shunt trip to the normally closed contacts from the Ansul system. It seems that every time I turn on the breaker for the Ansul system, both of the pizza oven breakers trip. Should I attach to the normally open contacts?
Should I wire the two pizza ovens in parallel or series?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#68804 - 08/16/06 06:55 PM Re: Shunt trip breakers
togol Offline

Registered: 09/15/05
Posts: 426
Loc: NW In. USA
around here, once the Ansul ring is pulled,
EVERYTHING electrical on
the cooking line must be de-energized,

the gas valve must close ,

the MUA for the hood is shut down,

and the hood exhaust fans shall continue to run....

is the Ansul system cocked ? it sounds like it is tripped and needs to be reset.

unwire the ansul switch and reset the shunt breaker , that should tell you

pizza ovens in parallel or series???

#68805 - 08/16/06 08:22 PM Re: Shunt trip breakers
Peter Offline

Registered: 06/08/04
Posts: 93
Loc: San Diego
The Ansul system is cocked.
What I mean by series/paeallel is there are two, three pole breakers, each with its' own shunt trip mechanism [takes up on breaker space]. I wired these in series instead of parallel.
What I need to know is what trips the shunt trip? Is it the presence of voltage or the absence?

#68806 - 08/17/06 03:14 AM Re: Shunt trip breakers
Roger Offline

Registered: 05/18/02
Posts: 1779
Loc: N.C.
The shunt trips work upon applied voltage.

You will need to wire two breakers in parallel.

One side of the shunt coils will wire to a neutral or neutral bar, (this is assuming 120 v shunt trip units) the other sides get the voltage through the Ansul switch. You will feed the Ansul common with 120 v and wire your switch leg to the open switch conductor when the Ansul system is cocked.


[This message has been edited by Roger (edited 08-17-2006).]

#68807 - 08/17/06 05:56 PM Re: Shunt trip breakers
Larry Fine Offline

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
Just an aside: For anyone who needs it, I came up with a way to interconnect the intake and exhaust fans to the control box using only 3 wires.

There are two advantages: (1) freeing up the second micro-switch for use with shunt-trips or other purposes; (2) being able to use simpler wiring methods (MC, etc. as required).

It can easily interface with existing wiring. Of course, anything other than 120v motors will need relays/contactors to use this method.



Larry Fine
Fine Electric Co.

#68808 - 08/18/06 08:20 AM Re: Shunt trip breakers
XtheEdgeX Offline

Registered: 04/17/05
Posts: 127
Loc: Florida
Normally Open

#68809 - 08/18/06 06:47 PM Re: Shunt trip breakers
Peter Offline

Registered: 06/08/04
Posts: 93
Loc: San Diego
Today I changed from serial to parallel. This seems to make sense. I had already changed from the N.C. contacts to the N.O. contacts.
Thank you for your adviCe.