The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 09:52 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
1 registered (geoff in UK), 213 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#68643 - 08/11/06 08:03 PM Re-posting high and low voltage problems
billy6139 Offline
New Member

Registered: 03/23/06
Posts: 9
Loc: Carson,Ca. USA
Reposting because topic was lost. I received one answer from Roger.

Scenario:Mobilehome park with 192 units. Main distribution is 240/120 3 wire from Edison. All main feeders are 100A 2 pole breakers feeding 4 to 8 pedestals with 50A mains. All distribution wiring is direct burial 1/0 aluminum, no conduits.
Problem: flucuating voltage. When loads are present(at times) voltage (between neutral or ground) on 1 leg lowers to 90 vbolts, while the other side increases to 140 volts. Voltage line to line is approximately 245 volts and fairly steady. This problem exist about 4 to 5 hundred feet away from main distrubution panel where voltage on the losd side of the breakers(at main distribution panel) remains 240/122, steady as a rock.
Has anyone ever experienced this? Any solutions?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#68644 - 08/11/06 11:15 PM Re: Re-posting high and low voltage problems
Larry Fine Offline

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
This is definitely an open neutral problem. The normally-zero-volts-to-ground on the neutral is being forced away from zero due to normal neutral current.

It can be a hazard because what should be grounded surfaces are instead being fed by the 25-or-so volts, and must be repaired ASAP.

Troubleshooting this would start with isolating the section with the broken line by finding the last point where the problem doesn't exist and the first point where it does.

Then start digging.
Larry Fine
Fine Electric Co.

#68645 - 08/12/06 08:09 AM Re: Re-posting high and low voltage problems
e57 Offline

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
I had the EXACT SAME PROBLEM, AND SCENARIO ten or so years ago.

I used to service work and had this, in a trailer park in Concord CA. Turned out to be a U/G direct burial feeder had a nick, and the AL conductor rotted over time.

To save on digging, put a tracer on the neutral and hope you get a dead end to the signal from both sides near the same spot. If you do thats were the Christy box goes. Becacuse it is intermitant they is no real guarantee it will would but well worth the shot!

Another method is to TDR the run, or use a pulse generator on the run. If you dont have any of the varied expensive equipment to find it, there are companies that specialize in it that you can sub it out too. Or you can rent it...
Mark Heller
"Well - I oughta....." -Jackie Gleason