#68515 - 08/09/06 04:52 PM romex in underground conduit
for2aflush Offline
Junior Member
Registered: 03/14/05
Posts: 5
Loc: riverton,nj,us
hello all, I'm trying to win a bet here. My boss said that you can run romex underground in condit . I said you need to run either U.F or thwn. he also said that thhn was fine in the ground as long as it is in conduit. we all know that romex isn't sutable for wet locations, but i cant find in the code that says that underground even in condit is a wet location .. any help would be apprecated . thanks
Top
Work Gear for Electricians and the Trades
#68516 - 08/09/06 06:04 PM Re: romex in underground conduit
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Look in the Definitions under "Location-Wet"

Also, THHN is not fine in the ground if it is in conduit. (I haven't seen any THHN only wire myself, only THHN/THWN)

Now do I get 1/2 the money you win?
Top
#68517 - 08/09/06 06:21 PM Re: romex in underground conduit
for2aflush Offline
Junior Member
Registered: 03/14/05
Posts: 5
Loc: riverton,nj,us
i will have to owe it to you ...lol thanks for your responce i looked up wet locations but it never said underground as one
Top
#68518 - 08/09/06 06:50 PM Re: romex in underground conduit
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
From Article 100, Definitions, in the 2005 NEC

Location, Wet. Installations under ground or in concrete slabs or masonry in direct contact with the earth..................

The definition is essentially the same in the 1940 NEC, too

[This message has been edited by electure (edited 08-09-2006).]
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 35 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals