The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Topic Options
Rate This Topic
#68350 - 08/03/06 12:56 PM ground testing
jay8 Offline
Member
Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
What is a ground resistivity test, and how does one go about testing a system ground?
Top
Work Gear for Electricians and the Trades
#68351 - 08/03/06 02:20 PM Re: ground testing
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
_________________________
Greg Fretwell
Top
#68352 - 08/03/06 02:23 PM Re: ground testing
hypress Offline
Member
Registered: 07/20/04
Posts: 132
Loc: Charleston WV
The most common way to test ground resistance is with a fall of potential tester some times called a earth megger.
It has 3 leads one goes to the ground rod under test,the second lead goes to a driven test electrode 60'from the rod under test and the 3rd driven test electrode is at 120'from the rod under test.All three of the points should be in a streight line. Now what happens is that a voltage is passed between the rod under test and the rod at 120'. The rod at 60' measures the voltage drop between the 60'point and the rod under test.The unit works on null balance an you adjust the 4 knobs until the zero center meter reads zero.The figure at the 12:00 on the knobs is the resistance of the ground.
A word of caution a new ground rod will have a higher resistance than one that has been in the ground for a couple of days.Let the earth heal around the rod before testing you will get a better reading.
Top
#68353 - 08/03/06 03:39 PM Re: ground testing
LK Offline
Member
Registered: 01/21/03
Posts: 1721
Loc: New Jersey
Service Upgrade $2000
Ground Testing $800

Be done with it, install the two rods!
Top
#68354 - 08/03/06 04:29 PM Re: ground testing
Roger Offline
Member
Registered: 05/18/02
Posts: 1779
Loc: N.C.
Along with Gfretwells link here is another one to check out.
http://www.tradeport.on.ca/ApplicationNotes/aemc.pdf

If this isn't a performance test required for a job specification, I would do as LK sugests and drive the second rod.

Roger
Top
#68355 - 08/03/06 05:02 PM Re: ground testing
LK Offline
Member
Registered: 01/21/03
Posts: 1721
Loc: New Jersey
Here in Jersey the public, and commercial pools, need a performance test, and inspection, there are companies that are set up for just that work.
Top
#68356 - 08/03/06 05:22 PM Re: ground testing
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
That's funny. I think the best electrode in the world is probably a gunite pool. You just can't call it that.

I have worked on several projects where they did performance testing of the grounding system. Mostly radio tower/equipment shelter installations and toll booths. The radio engineers design the tower systems and we had Bert Lavin (former CMP kinda guy)working on the tool booths. They turn out to be a lightning magnet around here.
_________________________
Greg Fretwell
Top
#68357 - 08/04/06 05:04 AM Re: ground testing
Zog Offline
Member
Registered: 09/13/05
Posts: 116
Loc: Charlotte, NC
To add to hypress description the center lead (Potential lead) should be placed at a distance that is 52% of the distance of the furthest lead (Current lead), record the value and move the center rod to 62%, record, then 72%, record. These values should be plotted to show a relativly flat line to verify your readings. If the plot is not flat your readings are being affected by the sphere of infulence of the ground rod under test and the current lead and the current lead should be moved further away from the rod under test and the entire procedure repeated until your 3 point plot is relativly flat.

Another method that is becoming more accepted is the clamp on method, simple and fast, but the test equipment is more expensive.
_________________________
MV/HV Testing Specialist, "BKRMAN"
Top
#68358 - 08/04/06 09:19 AM Re: ground testing
jay8 Offline
Member
Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
thanks for the feedback so far, FYI this is a commercial building, concrete encased grounding grid I believe, since the structure sits on a pier. Also 12.4kv coming in, with 4 2500kva transformers in the room.
Top
#68359 - 08/04/06 09:31 AM Re: ground testing
Zog Offline
Member
Registered: 09/13/05
Posts: 116
Loc: Charlotte, NC
You want to see less than 5 ohms for that type of system per NETA MTS
_________________________
MV/HV Testing Specialist, "BKRMAN"
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (sparkyinak), 96 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/01/07
Posts: 62

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals