Are those cheap 15A receptacles rated to be wired up as a pass-through for a 20A receptacle circuit? EG, put the wire in from panel on one screw, and out to the next rcpt on the other screw? There isn't any labeling on them to indicate that the jumper bar is rated for 20A, but I've seen this done before.
Top
Work Gear for Electricians and the Trades
#68278 - 08/01/06 01:55 PM Re: Wiring 15A Receptacles
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Yes, and you can find the info in the UL white book (General Directory)

If you really look at the same grade and brand 15 and 20 amp receptacles you will find the 'guts' are the same only the plastic face is different.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#68279 - 08/01/06 02:19 PM Re: Wiring 15A Receptacles
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Steve, I agree with Bob, and will add that if you are dealing with a multi-wire branch circuit the neutral must be pigtailed, see 300.13(B)

Roger
Top
#68280 - 08/01/06 04:44 PM Re: Wiring 15A Receptacles
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
Thanks guys, that makes it easy I only have 1 multiwire string in the whole house (two 240V 30A tool outlets in the shop) and was planning to pigtail it regardless!
Top
#68281 - 08/02/06 04:20 AM Re: Wiring 15A Receptacles
vlad_tepish Offline
Member
Registered: 10/30/05
Posts: 39
Loc: Delavan,Wis,USA
we always pigtail both hot and neut."pretend there is only one screw on each side"
_________________________
Patrick
Top
#68282 - 08/03/06 04:19 AM Re: Wiring 15A Receptacles
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Steve if your 240 volt tool circuit doesn't have a neutral, it's not a multiwire branch circuit.
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 35 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals