#68273 - 07/31/06 09:23 PM Single phase loads from a 3 phase...
Cinner Offline
Member
Registered: 12/01/04
Posts: 78
Loc: Kelowna, B.C., Canada
Can you share a neutral with three different single phase loads for example cccts 1,3,and 5 from a 3 phase load center? Lets say the the single loads are are three different receptacles. So can I pull a red, black and blue with one white wire to all threeand have each circuit share that neutral?
Top
Work Gear for Electricians and the Trades
#68274 - 07/31/06 09:38 PM Re: Single phase loads from a 3 phase...
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
You didn't say "wye" but it is assumed from the description and yes that is done all the time. These days it is recomended that you use "super neutral" cable if you are not sure what the loads will be. If they end up being reactive the triplen harmonics add on the neutral ... but I think we have already said that in another thread.
_________________________
Greg Fretwell
Top
#68275 - 08/01/06 07:12 AM Re: Single phase loads from a 3 phase...
MKD Steve Offline
Junior Member
Registered: 07/11/06
Posts: 6
Loc: Chicago, IL, USA
"Can you share a neutral with three different single phase loads for example cccts 1,3,and 5 from a 3 phase load center? Lets say the the single loads are are three different receptacles. So can I pull a red, black and blue with one white wire to all threeand have each circuit share that neutral?"

Yes you've created a 3 phase network. You would have to add a green wire if you really want to earn a gold star!
Top
#68276 - 08/01/06 09:48 AM Re: Single phase loads from a 3 phase...
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Yes, you can. Thats what 'multiwire circuits' are all about.

That said, the devil is in the details. As I've mentioned before in this forum, sharing a neutral can make things easire for the electrician (fewer wires to pull)- but also allows a few more opportunities for Mr. Murphy to work his mischief.

The main precaution to take is to be absolutely certain that your neutral connections are rock-solid.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals