#68269 - 07/31/06 07:15 PM Finding Grounds on Ungrounded Systems Energized
hypress Offline
Member
Registered: 07/20/04
Posts: 129
Loc: Charleston WV
I have seen a lot of verbage regarding locating grounds on ungrounded systems.I do this all the time WITHOUT shuting down equipment. Where I work we can not randomly shutdown equipment.
What we have is what we call a thumper. It is a 480V strip heater in series with a pulsing contactor and an 10amp analog meter.
To locate a ground we first determine which phase is grounded. Then we hook the unit up to one of the ungrounded and the other side to a good ground.Then we turn on the thumper on. It will generate a pulse inversley proportional to the quality of the ground. The current is read on the ammeter. Now a thong ammeter with a 0-20 amp scale with a jaw that fits around 4" conduit is snaped around each conduit or cable ALL THREE WIRES AT A TIME until the pulse is located . Then we follow the pulse until it stops. That is the where the ground is. With this equipment we can locate most grounds in 30 minutes or less. Some of our newer switchgear has ground locating pulsers built in it.
Top
Work Gear for Electricians and the Trades

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals