#68056 - 07/27/06 06:26 PM Flex 90
Gregtaylor Offline
Member
Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
Situation- 1" EMT from an MCC to a motor with 4 90 degree bends in the conduit. Changed over to flex for 24" for final connection and used a flex 90 connector at the motor. The inspector turned down the job because he says that's 5 bends in the run. If that's the interpretation I can show him thousands of violations. Any thoughts?
Top
Work Gear for Electricians and the Trades
#68057 - 07/27/06 06:44 PM Re: Flex 90
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Greg, unfortunately, per the pure wording of the conduit and tubing articles where it it states
Quote:
There shall not be more than the equivalent of four quarter bends (360 degrees total) between pull points, for example, conduit bodies and boxes.
the inspector is correct. You could use a condolet at the transition (if it stays accessible) and be compliant.

Roger
Top
#68058 - 07/27/06 07:06 PM Re: Flex 90
mister h Offline
Member
Registered: 05/26/06
Posts: 20
Loc: erie, pa. usa
You may need to check out 358.26 in the NEC code. This is where the code violation was from.

Ken
_________________________
ken
Top
#68059 - 07/27/06 07:11 PM Re: Flex 90
stamcon Offline
Member
Registered: 03/24/01
Posts: 329
Loc: So San Francisco CA
Roger, since you can't pull through a flex 90
*, should it be included as a bend between pull points? If there were 3 90* bends in the conduit and also the flex 90*, you still wouldn't be able to pull through the completed run. Just wondering...

steve
Top
#68060 - 07/27/06 07:47 PM Re: Flex 90
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Steve, very good point, and if I were the inspector I would conceed to your argument.

Roger
Top
#68061 - 07/28/06 03:56 AM Re: Flex 90
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Why not just use one of the 90° flex fittings with the sliding cover?
Try a Regal 9674
It adds 0° to your run.
Top
#68062 - 07/28/06 11:54 AM Re: Flex 90
Celtic Offline
Member
Registered: 02/26/05
Posts: 361
Loc: NJ
Quote:
Greg, unfortunately, per the pure wording of the conduit and tubing articles where it it states

:There shall not be more than the equivalent of four quarter bends (360 degrees total) between pull points, for example, conduit bodies and boxes.

the inspector is correct. You could use a condolet at the transition (if it stays accessible) and be compliant.

Roger

...BUT, the flex 90 IS a pull point

[This message has been edited by Celtic (edited 07-28-2006).]

[This message has been edited by Celtic (edited 07-28-2006).]
_________________________
~~ CELTIC ~~
...-= NJ =-...
Top
#68063 - 07/28/06 12:17 PM Re: Flex 90
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
How about all the "degrees of bend" in the flex whip? Does that count too?
_________________________
Greg Fretwell
Top
#68064 - 07/28/06 05:17 PM Re: Flex 90
Gregtaylor Offline
Member
Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
My view is that the 90 degree connector WITH A REMOVABLE BACK is a pull point just like an LB would be. I did not pull wire through it along with the other bends. I pulled out enough wire to reach the motor and fed that last 36" or so through the flex and through the connector. How many bends could there be in 24" of flex?
Top
#68065 - 07/28/06 07:12 PM Re: Flex 90
Peter Offline
Member
Registered: 06/08/04
Posts: 92
Loc: San Diego
Maybe 300-18 [1999 Code] may help in this situation. "The raceway shall be permitted to be initially installed without a terminating connection at the equipment."
The handbook notes that this applies to a 90º connection to a motor.
In any case, a 90º connector is impossible to pull under any circumstances. They must be hand fed one wire at a time and it takes an hour.
Note: the degree symbol "º" is made by Alt + 167. On the number keys with Num Lock and Scroll Lock on.
~Peter
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 14 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals