The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm▓ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
1 registered (cableguy619), 212 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#67913 - 07/21/06 01:51 AM Wire sizes
Kenbo Offline
Member

Registered: 04/07/06
Posts: 234
Loc: Scotland
Just looking at your posts here and often you mention wire gauge as 12/2 or 14/2 etc

Here in the UK we use cable like 2.5mm Twin&Earth (2.5T&E) or single cores 1.5mm.
Where the size stated is the diamiter of the copper core see here
How is cable sized where you are?
_________________________
der Gro├čvater

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#67914 - 07/21/06 02:30 AM Re: Wire sizes
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
AWG or American Wire Gauge.

14 AWG is rated approx 20 amps

12 AWG is rated approx 25 amps
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#67915 - 07/21/06 03:17 AM Re: Wire sizes
C-H Offline

Member

Registered: 09/17/02
Posts: 1508
Loc: Stockholm, Sweden
I've written a little on this, with some tables:
http://www.global-electron.com/wiresizes.htm

Top
#67916 - 07/21/06 03:46 AM Re: Wire sizes
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
T&E looks very similar to NM cable.

Interesting- 2.5mm T&E cable is smaller than #12, yet allowed for 24A circuits, whereas the larger #12 NM is only approved to 20A?

Top
#67917 - 07/21/06 07:24 AM Re: Wire sizes
Radar Offline
Member

Registered: 04/30/04
Posts: 349
Loc: Los Angeles, CA
I seem to remember hearing somewhere that metric amps are slightly smaller than non-metric, so that accounts for the difference in ampacity values.

kidding -
Radar
_________________________
There are 10 types of people. Those who know binary, and those who don't.

Top
#67918 - 07/21/06 09:42 AM Re: Wire sizes
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Actually 12 ga is good for 25a (310.16)
240.4(D) reduces that to 20a because the "small conductors" are most likely to serve receptacles where the installer has no control over what the user will plug in. They will keep plugging things in until the breaker trips, then unplug the clock. 240.4(D) forces the 80% rule on the user.
Perhaps Europeans are more dilligent about load management.
_________________________
Greg Fretwell

Top
#67919 - 07/23/06 06:45 AM Re: Wire sizes
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
 Quote:
Here in the UK we use cable like 2.5mm Twin&Earth (2.5T&E) or single cores 1.5mm.
Where the size stated is the diamiter of the copper core


Not the diameter -- 1.0, 1.5, 2.5 etc. are the cross-sectional area of the conductor, in square millimeters.

The pre-metric cables (before 1970) use a size designation based on the strand diameter, e.g. 3/.036 is a conductor consisting of three strands, each of .036" diameter.

Here is a comparison of American 12/2 w/gnd Romex and British 2.5 sq. mm "T&E" cable:







Note that the ground conductor on the U.K. cable is a size smaller than the insulated conductors, 1.5 sq. mm on this 2.5 cable.

You'll note also that British T&E doesn't have any paper inside the outer sheath like Romex.


[This message has been edited by pauluk (edited 07-23-2006).]

Top
#67920 - 07/23/06 08:13 AM Re: Wire sizes
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
OK, so it's more like UF! Is T&E rated for wet areas?

I'm going to have to pick up some samples of metric cable next time I'm over on that side of the pond...

[This message has been edited by SteveFehr (edited 07-23-2006).]

Top
#67921 - 07/23/06 05:19 PM Re: Wire sizes
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
#14 is 2.08 mm2
@12 is 3.31 mm2

Per table 8
_________________________
Greg Fretwell

Top
#67922 - 07/25/06 12:11 AM Re: Wire sizes
Kenbo Offline
Member

Registered: 04/07/06
Posts: 234
Loc: Scotland
Thanks for the replys all I can say is I learned something new today.

Paul thanks for the correction. I got my vernier gauge out and measured the diameter of some T&E cores
1mm = 1.1mm
2.5mm = 1.7mm
6mm = 3.1mm
(20 years and still making asumptions tut tut)

C-H managed to follow "AWG" and "Metric" but just could not see the point of "Circular Mils" Who uses "kcmil" as a measument?