#67735 - 07/13/06 08:08 PM Duct Detectors
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
Need some info on when they are needed if you don't mind..

Reason, HVAC contractor adding new RTU's. Existing RTU's have Duct detectors installed.
Wouldn't these new ones need these and be tied into the fire system?

Thx..
Top
Work Gear for Electricians and the Trades
#67736 - 07/14/06 03:24 AM Re: Duct Detectors
hypress Offline
Member
Registered: 07/20/04
Posts: 129
Loc: Charleston WV
Duct detectors are needed if the unit CFM rating is 2000 or greater on the return side.
If your unit is 4000 or greater you need them on supply and return. About the only thing they do is tell you that your duct has dust in it when the heat comes on.As far as early fire detection they are useless. Think about it you have a small fire in a room your HVAC is drawing clean air from other parts of the building when it gets back to the unit the air is so doluted there is no smoke to detect. But I know THE CODE REQUIRES THEM. I use to work for a fire alarn distributior we had Notifier and Pyrotronics equipment.
Top
#67737 - 07/14/06 06:21 AM Re: Duct Detectors
golf junkie Offline
Member
Registered: 04/22/01
Posts: 507
Loc: York, NE
I'm not that familiar with fire code so I can't say for sure what the code says.

We recently had a bid for a bank building, all smoke detection was removed because the building was sprinkled.
Top
#67738 - 07/14/06 07:47 AM Re: Duct Detectors
eprice Offline
Member
Registered: 08/07/03
Posts: 64
Loc: North Logan, Utah, USA
The requirement comes from the mechanical code. In the IMC it is found in section 606. There are a couple of exceptions there that will often apply. There will be a simular section in the UMC.
Top
#67739 - 07/14/06 08:28 AM Re: Duct Detectors
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
Depending on the applicable mechanical code, most require connection the the building fire alarm system for monitoring (if there is a building fire alarm system).
_________________________
Ron
Top
#67740 - 07/14/06 11:10 AM Re: Duct Detectors
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Dnk:
From the Fire Sub-Code Insp (NJ)here, exactly as Hypress said. IF system within structure it must be interconnected to provide notification.

In instances of nuisance activation (dust/humidity/etc) PERMISSION can be granted for local alarm only.

NOTE WORD "PERMISSION"

John
_________________________
John
Top
#67741 - 07/14/06 05:26 PM Re: Duct Detectors
Gregtaylor Offline
Member
Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
I would like to add that if the total CFM of all units in a discrete area (say a single tenant) is 2000 or more then the detectors are required. Not just the CFM of any one unit. They must be wired for unit shutdown and be monitored by the buildings central system. I'll quote NFPA when I find my book in this messy office.
Top
#67742 - 07/14/06 05:37 PM Re: Duct Detectors
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
Single building, single tennant.

30,000 Sq/ft

Had 5 RTU's initially, 5 more added.

The orginal 5 have (DD), but the newer ones do not.

Typical fire system installed, building is sprinklered, and has been since the orginal build.

Are they not needed if sprinklered then?
Top
#67743 - 07/14/06 06:20 PM Re: Duct Detectors
LK Offline
Member
Registered: 01/21/03
Posts: 1429
Loc: New Jersey
"Are they not needed if sprinklered then?"

Still need the detectors, the idea is to get notification, before the heat builds to trigger a sprinkler.
Top
#67744 - 07/15/06 08:21 AM Re: Duct Detectors
Gregtaylor Offline
Member
Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
Agree. Someone missed something somewhere.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals