#67177 - 06/28/06 01:55 PM Odd Circuit Breaker Behavior
wendel Offline
Member
Registered: 08/07/04
Posts: 55
I have a subpanel whose feed protected by two 30 amp old stlye (glass) fuses on each of the 120 volt lines.

In the subpanel is a 20 amp breaker for a pool pump.

The capacitor for the pool pump died and one of the 30 amp glass fuses blew.

My question is why didn't the 20 amp breaker trip before the 30 amp fuse blew?
Top
Work Gear for Electricians and the Trades
#67178 - 06/28/06 04:27 PM Re: Odd Circuit Breaker Behavior
Rewired Offline
Member
Registered: 01/01/06
Posts: 558
Loc: Hamilton, Ontario, Canada
Fuses in general especially if they are NOT time delay will open a circuit FASTER than a breaker will under a short circuit or severe overload condition, which I assume happened here..

A.D

[This message has been edited by Rewired (edited 06-28-2006).]

[This message has been edited by Rewired (edited 06-28-2006).]
Top
#67179 - 06/28/06 07:10 PM Re: Odd Circuit Breaker Behavior
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Sometimes a 100A CB (or > ) will pop before say a 20A CB, depending on the trip curve of the CB, or just the general condition of the CB....
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#67180 - 06/28/06 08:26 PM Re: Odd Circuit Breaker Behavior
jay8 Offline
Member
Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
Yes, it happens all the time where a branch circuit doesnt trip but the main does - whether a fuse or breaker. This is one of the reasons why its bad practice try to short out a circuit to identify it at the panel.
Top
#67181 - 06/28/06 11:13 PM Re: Odd Circuit Breaker Behavior
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Or NONE will trip at all....
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#67182 - 06/29/06 01:03 AM Re: Odd Circuit Breaker Behavior
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
Quote:
Or NONE will trip at all....


Been working with Federal Pacific recently?
Top
#67183 - 06/29/06 04:07 AM Re: Odd Circuit Breaker Behavior
Texas_Ranger Offline
Member
Registered: 12/17/01
Posts: 2391
Loc: Vienna, Austria
Oh, 1960s Schrack breakers (Austrian) were good at that too... few months ago I swapped out an entire panel at a friend's place because he complained dead shorts usually blew the 25A main fuse instead of the 10A breaker... the breaker was H characteristic, supposed to be much faster than a fuse.
Top
#67184 - 06/29/06 05:16 PM Re: Odd Circuit Breaker Behavior
WFO Offline
Member
Registered: 09/03/05
Posts: 202
Loc: Cat Spring, TX
Fuses tend to fatigue over time as well. They get weaker (particularly if they've been subjected to numerous faults) with age and will blow faster than their original published curves.
Top
#67185 - 06/29/06 09:52 PM Re: Odd Circuit Breaker Behavior
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
Quote:

My question is why didn't the 20 amp breaker trip before the 30 amp fuse blew?


Could be one, or more, of the following:

<OL TYPE=A>

[*] Fuse was Non-Time Delay type (Fast Acting),


[*] Terminations at the Fuse were generating heat, which assisted in a more rapid melting of the Fuse's element,


[*] Circuit Breaker's contacts are welded closed, from continuous reclosing on a faulted circuit,


[*] Circuit Breaker is of the infamous "FPE Trip-Free", or "No-Blow Zinsco" designs,


[*] Motor Circuit is maybe not fed "Entirely" through the 20 Amp Breaker,


[*] Non-Selective coordination between the Feeder's OCPD and the Panelboard's OCPD.
</OL>

Sounds more likely that the Fuse was just a Fast Acting type.

At least the E base Fuse did not have a
"Capacity Extending Device"
or
"Trip Eliminator"
(AKA "Coin behind the Fuse")


Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#67186 - 06/30/06 02:43 PM Re: Odd Circuit Breaker Behavior
Rewired Offline
Member
Registered: 01/01/06
Posts: 558
Loc: Hamilton, Ontario, Canada
HEY NOW!
Easy on the FPE my place is full of it

( and believe it or not they DO work!!)

A.D
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 56 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals