#66663 - 06/12/06 07:20 PM Can't get there from here!
arseegee Offline
Member
Registered: 01/28/02
Posts: 324
Loc: Statesboro, GA USA
Just wondering how you guys might tackle this. I am doing the build outs on a few retail stores in a new strip center. We start a sunglass hut tomorrow.

Here's the question. CG that handled the erection and exterior work of the structure had an EC run the pipe for service laterals back to the xmfmr pads. All lateral pipes are 4" EPVC. Well all our services are only 200A and POCO requires us to use their can which only goes to 2.5" on the bottom KO's.

I wont go into how bad the pipes are out of plumb... it's a real mess.

I have seen this done with PVC (water pipe) reducing bushings and it looks like a hack job. Any advice on how to get from 4" to 2.5" and have it look respectable?
Top
Work Gear for Electricians and the Trades
#66664 - 06/12/06 08:24 PM Re: Can't get there from here!
JCooper Offline
Member
Registered: 12/30/02
Posts: 228
Loc: Kendall Park, NJ USA
Any chance of putting a gutter between your lateral and the poco can?
Top
#66665 - 06/13/06 06:45 AM Re: Can't get there from here!
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
I would consider installing a flush handhole a couple of feet out from the hut. If the dirt is already paved, then, I would consider a "C" condulet with a reducing bushing. You did indicate the riser is not too plumb. So, maybe the gutter idea is the only one that will work.
_________________________
Earl
Top
#66666 - 06/13/06 08:20 AM Re: Can't get there from here!
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Assuming that EPVC is electrical PVC conduit, then Carlon makes a 4 x 3 bell reducer. Maybe you could use that along with a 3 x 2.5 PVC reducing bushing.
Don
_________________________
Don(resqcapt19)
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals