#66379 - 05/31/06 11:53 PM is it up to the inspector?
drgnz23 Offline
Member
Registered: 02/17/02
Posts: 56
Loc: los angeles
Okay im doing a 200 amp service change.
(1)Does my ground have go from the panel to the main water line then to my ground rod or can i save some money and start with the ground rod first ? Considering prices are so high for coppper i dont want to back track my ground and use another 50 ft...
Top
Work Gear for Electricians and the Trades
#66380 - 06/01/06 01:28 AM Re: is it up to the inspector?
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8560
Loc: SI,New Zealand
Did you bid too low?.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#66381 - 06/01/06 03:39 AM Re: is it up to the inspector?
je1ff Offline
Junior Member
Registered: 07/16/04
Posts: 1
Don't you run a seperate ground from the panel to each? You only need #6 to the rod, and you need #4 for the waterpipe.
Top
#66382 - 06/01/06 04:26 AM Re: is it up to the inspector?
steve ancient apprentice Offline
Member
Registered: 03/04/05
Posts: 170
Loc: west springfield,mass
I totally agree with je1ff. #6 wire to the ground rods and # 4 to the water pipe with proper clamps to jump the meter. Have never seen it done any other way. Years ago they just ran it to the water meter but not today.
Top
#66383 - 06/01/06 06:56 AM Re: is it up to the inspector?
BigB Offline
Member
Registered: 03/31/04
Posts: 727
Loc: Tucson, AZ USA
Where 2 rods are required, would it be NEC compliant to run 2 GEC's from the main bus, one to each rod?
Top
#66384 - 06/01/06 07:37 AM Re: is it up to the inspector?
Roger Offline
Member
Registered: 05/18/02
Posts: 1779
Loc: N.C.
You can run a propper sized (largest required for the sevice) GEC to the first electrode and use jumpers to bond all the rest together.



Although it is okay to run a seperate GEC to each GE it is not necessary, see 250.50

Roger
Top
#66385 - 06/01/06 07:57 AM Re: is it up to the inspector?
macmikeman Offline
Member
Registered: 07/16/02
Posts: 718
Loc: Honolulu, Hawaii
Nice drawing Roger. May I add the word "Interior" to the blue colored note? 250.52

[This message has been edited by macmikeman (edited 06-01-2006).]
Top
#66386 - 06/01/06 08:09 AM Re: is it up to the inspector?
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 4196
Loc: NY, USA
For what it's worth our local POCO requires a separate GEC to each rod.

Bill
Top
#66387 - 06/01/06 08:51 AM Re: is it up to the inspector?
Roger Offline
Member
Registered: 05/18/02
Posts: 1779
Loc: N.C.
Thanks Mike, but I can't take the credit, the drawing is out of the handbook.

As Bill points out, sometimes there are rules outside of the NEC or local electrical codes that we must follow.

Roger
Top
#66388 - 06/01/06 02:39 PM Re: is it up to the inspector?
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
I tend to disagree with the handbook drawing in this instance. The last sentance of 250.53(D)(2) states that a supplemental electrode must be bonded to:
1) The GEC,
2) The service nuetral,
3) The service conduit, or
4) A grounded service enclosure.

One of the electrodes in the handbook drawing MUST be called a supplement, and bonding the supplemntal electrode to the water pipe is not one of the 4 options listed above, as per 250.53(D)(2).
_________________________
Ryan Jackson,
Salt Lake City
Top
Page 1 of 3 1 2 3 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
01/23/17 12:27 AM
License exam
by TRUE POWER
01/22/17 11:33 PM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
2 registered (sparkyinak, Admin), 81 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals