The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 216 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#65926 - 05/16/06 06:03 PM 15 amp circuit in commercial?
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
Has anyone seen or installed 15 amp circuits in commercial buildings? I have never seen one, only 20 amp and up.
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#65927 - 05/16/06 06:20 PM Re: 15 amp circuit in commercial?
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
Not a common pratice to say the least....
Off the top of the head, can't see why not either.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#65928 - 05/16/06 06:40 PM Re: 15 amp circuit in commercial?
BigJohn Offline
Member

Registered: 03/06/04
Posts: 352
Loc: Boston, MA
The answer I picked up somewhere was that commercial systems generally have a higher AFC than residential. During a fault, less chance the #12AWG would fail than the #14.

However, seems to me properly sized and coordinated OCPDs would do their job and protect #14 just as well as #12. Not sure 5 amps makes all that much difference, anyway.



-John

[This message has been edited by BigJohn (edited 05-16-2006).]

Top
#65929 - 05/16/06 07:57 PM Re: 15 amp circuit in commercial?
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I suspect it has more to do with the fact that you have the 180va per outlet restriction in commercial (and perhaps that there is not usually much #14 on a commercial wire cart). It would make sense if this was a dedicated circuit for some low current equipment though. From a safety standpoint, oversizing a circuit (and OCP device) is not always a good idea.
_________________________
Greg Fretwell

Top
#65930 - 05/16/06 07:59 PM Re: 15 amp circuit in commercial?
GEC-1 Offline
Member

Registered: 06/06/01
Posts: 32
Loc: Covington, Georgia USA
Yes! I have put 15 amp ckts. in commercial! I wired a pool house for an apartment complex, and used #14 for several of my lighting ckts. Code does allow this.

Top
#65931 - 05/16/06 08:26 PM Re: 15 amp circuit in commercial?
DougW Offline
Member

Registered: 06/08/03
Posts: 1083
Loc: North Chicago, IL
Our local addendums specifically prohibit it.

Top
#65932 - 05/17/06 02:49 AM Re: 15 amp circuit in commercial?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
GEC-1 what you describe is not IMO commercial.

That said the NEC certainly does not prohibit it.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#65933 - 05/17/06 07:36 AM Re: 15 amp circuit in commercial?
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
The reason I ask is someone added some walls and wired some church offices in
14-2 romex. Probably be ok, not much load there. The walls are wood construction too. I could change the breaker to a 15 amp.
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
#65934 - 05/17/06 11:13 AM Re: 15 amp circuit in commercial?
IanR Offline
Member

Registered: 12/06/04
Posts: 326
Loc: Palm Bay FL USA
I work at a very large industrial manufacturer and we have many 15A circuits. While many locales prohibit it. I think often times, it is just a matter of how the wiring is spec'd rather than an NEC issue.

[This message has been edited by IanR (edited 05-17-2006).]

Top
#65935 - 05/17/06 12:05 PM Re: 15 amp circuit in commercial?
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Aldav53, I need some clarification, in your first post you ask,
 Quote:
Has anyone seen or installed 15 amp circuits in commercial buildings?
and then in your second post you say,
 Quote:
The reason I ask is someone added some walls and wired some church offices in 14-2 romex. Probably be ok, not much load there. The walls are wood construction too. I could change the breaker to a 15 amp.


What you appear to have is # 14 over fused and in violation of 240.4(D), you must change the breaker(s)

With that said, there is no problem as far as the NEC is concerned with having 15 amp circuits in commercial installations if the wiring meets or exceeds the OCPD.

Even in areas where #12 is the minimum size conductor for branch circuits or feeders it would not prohibit protecting the conductors at 15 amps or lower, and infact, certain equipment may have a Max circuit protection below 15.

Roger

Top