#65926 - 05/16/06 06:03 PM 15 amp circuit in commercial?
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
Has anyone seen or installed 15 amp circuits in commercial buildings? I have never seen one, only 20 amp and up.
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
Work Gear for Electricians and the Trades
#65927 - 05/16/06 06:20 PM Re: 15 amp circuit in commercial?
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Not a common pratice to say the least....
Off the top of the head, can't see why not either.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#65928 - 05/16/06 06:40 PM Re: 15 amp circuit in commercial?
BigJohn Offline
Member
Registered: 03/06/04
Posts: 391
Loc: Boston, MA
The answer I picked up somewhere was that commercial systems generally have a higher AFC than residential. During a fault, less chance the #12AWG would fail than the #14.

However, seems to me properly sized and coordinated OCPDs would do their job and protect #14 just as well as #12. Not sure 5 amps makes all that much difference, anyway.



-John

[This message has been edited by BigJohn (edited 05-16-2006).]
Top
#65929 - 05/16/06 07:57 PM Re: 15 amp circuit in commercial?
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I suspect it has more to do with the fact that you have the 180va per outlet restriction in commercial (and perhaps that there is not usually much #14 on a commercial wire cart). It would make sense if this was a dedicated circuit for some low current equipment though. From a safety standpoint, oversizing a circuit (and OCP device) is not always a good idea.
_________________________
Greg Fretwell
Top
#65930 - 05/16/06 07:59 PM Re: 15 amp circuit in commercial?
GEC-1 Offline
Member
Registered: 06/06/01
Posts: 32
Loc: Covington, Georgia USA
Yes! I have put 15 amp ckts. in commercial! I wired a pool house for an apartment complex, and used #14 for several of my lighting ckts. Code does allow this.
Top
#65931 - 05/16/06 08:26 PM Re: 15 amp circuit in commercial?
DougW Offline
Member
Registered: 06/08/03
Posts: 1143
Loc: North Chicago, IL
Our local addendums specifically prohibit it.
Top
#65932 - 05/17/06 02:49 AM Re: 15 amp circuit in commercial?
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
GEC-1 what you describe is not IMO commercial.

That said the NEC certainly does not prohibit it.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#65933 - 05/17/06 07:36 AM Re: 15 amp circuit in commercial?
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
The reason I ask is someone added some walls and wired some church offices in
14-2 romex. Probably be ok, not much load there. The walls are wood construction too. I could change the breaker to a 15 amp.
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
#65934 - 05/17/06 11:13 AM Re: 15 amp circuit in commercial?
IanR Offline
Member
Registered: 12/06/04
Posts: 328
Loc: Palm Bay FL USA
I work at a very large industrial manufacturer and we have many 15A circuits. While many locales prohibit it. I think often times, it is just a matter of how the wiring is spec'd rather than an NEC issue.

[This message has been edited by IanR (edited 05-17-2006).]
Top
#65935 - 05/17/06 12:05 PM Re: 15 amp circuit in commercial?
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Aldav53, I need some clarification, in your first post you ask,
Quote:
Has anyone seen or installed 15 amp circuits in commercial buildings?
and then in your second post you say,
Quote:
The reason I ask is someone added some walls and wired some church offices in 14-2 romex. Probably be ok, not much load there. The walls are wood construction too. I could change the breaker to a 15 amp.


What you appear to have is # 14 over fused and in violation of 240.4(D), you must change the breaker(s)

With that said, there is no problem as far as the NEC is concerned with having 15 amp circuits in commercial installations if the wiring meets or exceeds the OCPD.

Even in areas where #12 is the minimum size conductor for branch circuits or feeders it would not prohibit protecting the conductors at 15 amps or lower, and infact, certain equipment may have a Max circuit protection below 15.

Roger
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals