#65873 - 05/15/06 07:19 AM Air Handler Exhaust during fires.
rad74ss Offline
Member
Registered: 04/19/04
Posts: 156
Loc: Pryor, OK USA
Many of you on this forum have firefighting experience. On rooftop air handlers with direct exhaust who decides what the unit does when the fire alarm goes off? Is it specific to the city or building?

Is it best to have the air handler exhaust smoke until the fire department cuts power? Would it depend on the estimated time to evacuate the building? Say run the exhaust for 45 minutes if it takes 30 minutes to evacuate the building? These are the same questions I am asking our customer but I would like to see the different applications and their effects that people have seen in real world applications.

I also know there are so many variables involved that it becomes complicated. From my Navy firefighting days I remember ventilating the compartment with a hatch, then someone opens a hatch on the other side and it creates a blow torch effect.

I would appreciate hearing your views on this application.
Top
Work Gear for Electricians and the Trades
#65874 - 05/15/06 11:27 AM Re: Air Handler Exhaust during fires.
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
If it is only exhaust, then it would depend on whether smoke control is required by the mechanical code. If smoke control is not required, then there is no requirement to shut down an exhaust only fan .
_________________________
Ron
Top
#65875 - 05/15/06 01:31 PM Re: Air Handler Exhaust during fires.
NJ_WVUGrad Offline
Member
Registered: 01/17/06
Posts: 47
Loc: Neptune, NJ, USA
Based on my experiences in NJ

The BOCA Code calls for a duct mounted smoke detector to shut down an air handler for any unit 5-Tons Nominal and over.
Top
#65876 - 05/15/06 02:52 PM Re: Air Handler Exhaust during fires.
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Rad:
Are you talking about kitchen exhaust hoods? or HVAC equipment??

Kitch exhaust hoods, exhaust "on", MUA 'OFF' for fire activation

John
_________________________
John
Top
#65877 - 05/15/06 03:55 PM Re: Air Handler Exhaust during fires.
jdevlin Offline
Member
Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
I asked the same question because we have two offices. One the HVAC shuts down on fire alarm the other it does not.
One building has two floors the other is single floor. I was told HVAC only needs to shut down on two story or up buildings. This is in Ontario Canada.
Top
#65878 - 05/15/06 06:48 PM Re: Air Handler Exhaust during fires.
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
NJ_Grad,
I believe that New Jersey statewide goes by the 2003 International Mechanical Code. Smoke control systems are handled by Section 513, which is a special animal regarding when it goes on or off.
Section 606 is where duct detectors are required, which identify return or common supply and return locations requiring shutdown. There is no mention of exhaust.
_________________________
Ron
Top
#65879 - 05/15/06 08:25 PM Re: Air Handler Exhaust during fires.
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
This is where the engineer / archetect earns his pay. The question of "to vent or not to vent" is decided in conjunction with other parts of the system.

While kitchen hoods always get shut down, I have seen major public buildings where a fire alarm will both close fire doors AND turn on major exhaust fans.
Top
#65880 - 05/15/06 08:38 PM Re: Air Handler Exhaust during fires.
NJ_WVUGrad Offline
Member
Registered: 01/17/06
Posts: 47
Loc: Neptune, NJ, USA
Ron,
Understood

With Mechanical it really breaks down to using the correct terminology.

I read "Rooftop Air Handlers" as a Packaged Rooftop Unit (RTU), it didn't sound like he was reffering to a smoke control system.

Just depends on what rad74ss was refering to.

thanks on the specifics though
Top
#65881 - 05/16/06 04:17 AM Re: Air Handler Exhaust during fires.
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
John,
Quote:
While kitchen hoods always get shut down,

Many times the exhaust hood stays on to pull the extinguishing agent up the duct.
Don
_________________________
Don(resqcapt19)
Top
#65882 - 05/16/06 05:56 AM Re: Air Handler Exhaust during fires.
rad74ss Offline
Member
Registered: 04/19/04
Posts: 156
Loc: Pryor, OK USA
This is an HVAC air handler with a split condensing unit. The fire alarm turns of the heater and/or the supply air blower. There are two exhaust fans blowing out horizontally on the left and right sides of the return air stack.

The whole unit can be disabled by a remote signal and of course disconnecting main power. It is currently set up to stop the supply blower and vent smoke with the exhaust fans until the unit is disabled. The customer has not responded yet on what they require and if their fire system can disable the unit if the fire is directly in the zone the air handler supplies.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals