The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 11:04 PM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 6
renosteinke 6
Potseal 4
Who's Online
0 registered (), 221 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#65575 - 05/06/06 01:35 PM Series Ratings
SolarPowered Offline

Registered: 07/05/04
Posts: 615
Loc: Palo Alto, CA, USA
It was mentioned in another thread that, in some areas, municipalities and some POCOs are requiring a 22kA rating on residential services.

I've read Sq D's and C-H's documents on series ratings, and their panels are specified and tested such that a 22kA or 25kA main breaker in series with a 10kA branch-circuit breaker has an overall 22kA series rating.

But, these series ratings don't extend to three in a row. If you have a subpanel fed from a 10kA feeder breaker, those 10kA breakers in the subpanel aren't covered in the listing for the series rating; they only have their native 10kA rating.

To get to 22kA, you need to do one of two things: Either use a 22kA breaker for the feeder, or use 22kA breakers in the subpanel.

What I'm wondering is, what are people actually doing on subpanels in the areas that are requiring 22kA residential equipment? Are you installing 22kA feeder breakers, or just assuming that the 22kA main covers the whole thing?

Or is my understanding of three-in-a-row series ratings incorrect?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#65576 - 05/07/06 12:18 AM Re: Series Ratings
e57 Offline

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
My understanding is that the 22K main to 10K branch would be the same as a 22K main to 10K feeder to 10K branch.

OR- 22K main to 22K feeder to 10K branch.

Most of the lists, in panels or other documentaion I have seen, seem to reflect that.

And would accomplish the same thing. Really depends on the list of allowable breakers.... (Which seem to be, any that THEY make. )

What I have always wanted to know is. If Company A claims thier 22k breaker will accomadate 22k for the 10k breaker of Company A. Why would it not withstand 22K for Company B's 10K breaker?
Mark Heller
"Well - I oughta....." -Jackie Gleason

#65577 - 05/07/06 02:09 PM Re: Series Ratings
Ron Offline

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
I'm not aware of any maximum distance requirements between series rated devices, or a requirement to be directly adjacent in the distribution path.
If there is a fault downstream of the second 10kAIC breaker, the current will come from the first 22kAIC rated breaker and act appropriately.
Be sure there is no significant motor load downstream, because then the fault current downstream may be different than that seen upstream.

#65578 - 05/07/06 03:14 PM Re: Series Ratings
JBD Offline

Registered: 07/12/01
Posts: 599
Loc: WI, USA
Series ratings must be tested. I have never seen a tested rating on any "classified" breaker.

It is possible to have series ratings of 3 breakers. You can not "skip" a sub-feed breaker it must have been tested.

edit: changed to classifed

[This message has been edited by JBD (edited 05-07-2006).]

#65579 - 05/07/06 09:43 PM Re: Series Ratings
mxslick Offline

Registered: 10/24/04
Posts: 785
Loc: Atomic City, ID USA
Stupid should be painful.