#65443 - 05/03/06 04:01 AM 208 v. 240... again!
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
We know that motors can tolerate = / - 10% voltage variation. That math is simple enough on a dual-voltage motor (230 / 460, 120 / 230).

What if the motor is rated 120 / 208-230.
What is the actual permitted deviation at the higher voltage.
Can you apply the tolerance to the whole range?
For example, supplying the motor with 240 volts would still be less than 10% above 230, but it will be more than 10% above 208.
Top
Work Gear for Electricians and the Trades
#65444 - 05/03/06 07:35 AM Re: 208 v. 240... again!
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
That means the motor will operate on any voltage within that range; in this case, anywhere between 208 and 230, as well as 10% below 208 and above 230. In my opinion, the 240 will be satisfactory.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#65445 - 05/03/06 02:23 PM Re: 208 v. 240... again!
Dave T Offline
Member
Registered: 01/22/05
Posts: 155
Loc: Waukesha, WI, USA
Remember that 240v is a nominal voltage and the actual voltage where the motor is to be most likely will be close to 230v.
How many motors are labeled 480v? Most are 460v.
Top
#65446 - 05/03/06 06:01 PM Re: 208 v. 240... again!
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
When an appliance -such as a motor- is given an operating range on the nameplate, the entire range is used.

For example, a motor rated 208-230 (on the nameplate) would have been tested at -10% of 208, and +10% of 240.

An important consideration, however, is that the testing criteria only require that nothing bad immediately happen. Long-term over-heating, inefficiency, and a dramatic loss of torque are all allowed, and not even looked for!
Top
#65447 - 05/04/06 01:55 AM Re: 208 v. 240... again!
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
In the term of the art:

Supply/ Line voltage of 240 is considered equal to ...

Motor/ Load voltage of 230.

These terms refer to the exact same system.

208V supplies are to feed 200V motors.

All of these terms are NOMINAL.

ie they are NEVER expected to be exact. If you get close... you're okay.
_________________________
Tesla
Top
#65448 - 05/04/06 08:35 AM Re: 208 v. 240... again!
SolarPowered Offline
Member
Registered: 07/05/04
Posts: 625
Loc: Palo Alto, CA, USA
Dumb question: Does anything bad happen when you increase the voltage to a synchronous motor? For example, if you had a 230/240V or whatever it is motor, and ran it at, say 300V, does that cause any problems?

Motors are, obviously, different from light bulbs. Increase the voltage feeding a light bulb, and the current increases, the power increases as the square of the voltage increase (not counting the temperature dependence of the filament, which is huge), all of which results in a large increase in brightness and a very short lifetime.

A synchronous motor, on the other hand, tends to draw whatever power is needed to rotate the load. If you increase the voltage to it, it's just going to cause a slight change in the phase angle between rotating vector and the nominal "no load" position, so that after you figure in the change in power factor, it's drawing pretty much the same power as before. At least that's how is seems to me.

Beyond synchronous motors, I don't have a mental picture for other types of motors, so I don't even have a theory on how voltage effects them.

Any thoughts on any of this?


[This message has been edited by SolarPowered (edited 05-04-2006).]
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (cableguy619), 64 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals