The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Safety at heights?
by gfretwell
Today at 02:19 AM
Looking for older post
by Trumpy
Today at 01:04 AM
Last time to chat here
by Trumpy
Yesterday at 11:41 PM
Unsafe Situations
by Trumpy
Yesterday at 09:46 PM
Webmaster > Admin
by Trumpy
Yesterday at 08:29 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Trumpy 19
Ruben Rocha 17
gfretwell 16
Who's Online
1 registered (Ruben Rocha), 174 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#65388 - 05/01/06 09:08 PM Circuit Breakers
96mystic Offline
Junior Member

Registered: 05/01/06
Posts: 1
Loc: Gresham, Oregon, USA
When sizing a circuit breaker, is it fair to say: multiply the calculated amperage by 1.25 and, if necessary, round up?
Thanks in advance,
Jim Finley
_________________________
"Tell me, I'll forget".
"Show me, I'll remember".
"Involve me, I'll understand".

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#65389 - 05/01/06 09:12 PM Re: Circuit Breakers
frenchelectrican Offline


Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
gernally yes but a catch is it depend on the conductor as well

devices 800 amp and over

where the over current device is rated 800 amp and over the conductors ampcity it protected shall be equal or greater than rating of conductors

device of 800 amp or less
the next stanard overcurrent rating shall be permitted to be used provied all the following condtion are met:

1] the conductors being protected are not part of multioutlet branch circuit supplying for cord and plug connected portable loads

2] the ampacity of the conductors does not corponded with the standard ampre rating of the fuse or circuit breaker without overload adjustment above the ratings

3] the next higher standard rating do not excess of 800 amperes. [ see above ]

merci, marc

[This message has been edited by frenchelectrican (edited 05-02-2006).]
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#65390 - 05/02/06 03:03 PM Re: Circuit Breakers
Dave T Offline
Member

Registered: 01/22/05
Posts: 157
Loc: Waukesha, WI, USA
It's simple. Calculate the load (125%+100%), select a cable to carry the load (the cable must carry the calculated load), select a breaker to protect the cable (the breaker is based upon the cable's rated ampacity noting the 800a up/down rule as the other poster pointed out).

Top