The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Why cables look like they do
by Texas_Ranger
38 minutes 9 seconds ago
Forum Software Upgrade coming soon...
by HotLine1
42 minutes 36 seconds ago
Re: Fabricating Guards out of Lexan?
by ghost307
Today at 11:21 AM
Would ELV branch circuits be a good idea?
by ghost307
Today at 11:18 AM
100% breakers?
by Texas_Ranger
Yesterday at 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 19
Webmaster 14
Trumpy 12
ghost307 12
frank 9
Who's Online
2 registered (gfretwell, ghost307), 0 Guests and 80 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#64705 - 04/12/06 03:31 PM GEC with (2) 200AMP Main Disconnects
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
I'm taking over a job that someone else started and had a question about jumping a GEC from one main disconnect panel to another main disconnect panel. Both panels are 200 amps each and are side by side. As it is now, the one GEC that comes from the water main is terminated in one panel, and jumped out to the other panel. Something tells me this wrong and that the GEC should be "tapped" before entering either of the panels. I'm not sure wich article applies here. Any help would be appreciated.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#64706 - 04/12/06 04:22 PM Re: GEC with (2) 200AMP Main Disconnects
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
250.64(C) requires a continuous (unspliced) GEC unless spliced by an irreversible compression connector.
250.64(D) pemits taps to a GEC where multiple service enclosures are installed.

If you enter the first enclosure and then run a jumper to the second one, it could be argued that the GEC to the second one is not continuous because it is "extended" (to the second panel) without the use of an irreversible comnpression connector as required by 250.64(C).
On the other hand, entering the first enclosure with #2, then jumping to the 2nd enclosure with #4, seems no different than tapping onto a #4 with a mechanical connector, which is acceptable for the tap (but not a splice)
It seems easier to just run an appropriately sized GEC (#2) beneath or above each enclosure and tap on a #4 to each ground buss.

[This message has been edited by Redsy (edited 04-12-2006).]

[This message has been edited by Redsy (edited 04-13-2006).]

Top
#64707 - 04/13/06 05:08 PM Re: GEC with (2) 200AMP Main Disconnects
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
Thank you, Redsy! That's exactly what I thought was the right thing to do, but I needed to know the article I was thinking of. I was looking past 250.66 for what I needed. The #4 copper to the water meter also needs to be upgraded to the appropriate size for the 300 amp feed at the meter pan. Thaks for your help, I really appreciate it.