#64657 - 04/11/06 03:18 PM water in conduit
scameron81 Offline
Member
Registered: 02/24/04
Posts: 75
Loc: Healdsburg, ca, USA
We are having a problem with water coming out of a 1" conduit in a pool house. There is a christy box uphill from the poolhouse that the pipe comes from. Now we are having water problems and the inspector won't pass us until we rectify the situation. My boss says there are some special pipe plugs that you can get to seal the pipe. I can't seem to find them anywhere. I was hoping that someone could shed some light on the subject. For the record we didn't install the conduit, the superintendant did, but of course he doesn't remember that now. How convienent.
Top
Work Gear for Electricians and the Trades
#64658 - 04/11/06 04:18 PM Re: water in conduit
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Try checking OZ Gedney, they have some pretty nice seals although I'm not sure if they address this exact application.

You may be able to get plain old Duct Seal to work.
http://www.o-zgedney.com/PDF/PA1[1].pdf


Roger



[This message has been edited by Roger (edited 04-11-2006).]
Top
#64659 - 04/11/06 05:39 PM Re: water in conduit
LK Offline
Member
Registered: 01/21/03
Posts: 1429
Loc: New Jersey
"For the record we didn't install the conduit, the superintendant did"

____________________________________________

Sounds like the super, has some work to do.
Top
#64660 - 04/11/06 06:14 PM Re: water in conduit
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
LK, the problem is
Quote:
but of course he doesn't remember that now.
once we get him to remember he may indeed have some work to do.

Roger
Top
#64661 - 04/11/06 07:59 PM Re: water in conduit
mhulbert Offline
Member
Registered: 10/19/04
Posts: 132
Loc: Anaheim, CA USA
Dig up your conduit and put another Christy box w/ a gravel drainage bed under it right before the pipe goes inside your building.

This is a "water trap", sort of the reverse of a plumbers trap. Standard issue if you have big hills and pipe going into buildings or equipment.
Top
#64662 - 04/11/06 11:18 PM Re: water in conduit
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
mhulbert's idea is a good one, short of installing a sump pump. It may very well work, so long as that drainage in the Chisty does not saturate.

Is the water from run off, or ground water below the surface?

If run off, you can extend the conduit higher up in the Chisty and seal it, so it doesn't act like sink drain, and improve the drainage in that box.

If it's ground water, and the slightest leak in the conduit you may be SOL. You have few options, locate the leak, and fix it. Or abandon it, and start fresh. You still need to stop the water, right? Mix up a slurry of cement, (portland milk-shake) cork the end at the house, fill, and start over. 100' of 1" may take 100lbs, and 50 gal of water to fill with slurry, but you only need to the end at the house, so maybe less... Too bad you can't still use the conductors and pipe after that. I grouted some clay voids in my yard that way, and it worked great at stopping the water.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#64663 - 04/12/06 05:09 PM Re: water in conduit
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
Immediately upon entering the pool-house, install a PVC box on the 1 inch conduit. A 1/2 inch PVC conduit drain out the bottom, and the continuation of the 1 inch run out the top should fix the problem. Run the PVC conduit drain to the floor drain, or through the wall to drain like an AC condensate drain.
_________________________
Earl
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals