The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Would ELV branch circuits be a good idea?
by Texas_Ranger
24 minutes 10 seconds ago
100% breakers?
by Texas_Ranger
28 minutes 26 seconds ago
Forum Software Upgrade coming soon...
by Trumpy
01/14/17 07:11 PM
Faricating Guards out if Lexan?
by Trumpy
01/14/17 07:09 PM
Dangerous DIY Advice
by Potseal
01/12/17 09:52 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 15
gfretwell 11
ghost307 10
sparkyinak 10
Trumpy 8
Who's Online
2 registered (LongRunner, Texas_Ranger), 288 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#64462 - 04/07/06 10:35 PM Tie handles
GTE Offline
Member

Registered: 03/26/03
Posts: 48
Loc: Bridgehampton, N.Y. USA
When are tie handles between single pole circuit breakers not approved?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#64463 - 04/08/06 10:52 AM Re: Tie handles
Dave T Offline
Member

Registered: 01/22/05
Posts: 157
Loc: Waukesha, WI, USA
ANS: When a "common trip" breaker is required by the NEC.
Handle ties are only used when one wants to assure that (2) adjacent 1p breaker are to be manually opened and closed at the same time.
Handle ties ARE NOT A SUBSITUTE for 2p or 3p common trip breakers that look like they are tied together with only a handle tie.

Top
#64464 - 04/08/06 01:00 PM Re: Tie handles
ctardi Offline
Member

Registered: 03/27/06
Posts: 15
Loc: Maple Ridge, BC, Canada
So, you could use them in a situation where two outlets in the same box are on different circuts?
_________________________
Proud Inventor of the Three Phase Light Bulb!

Top
#64465 - 04/08/06 03:29 PM Re: Tie handles
Alan Nadon Offline
Member

Registered: 03/10/05
Posts: 398
Loc: Elkhart, IN. USA
See NEC 210.4 (B) 2002.
If they share a common grounded conductor they must be 2 pole not handle tied.
Alan--
_________________________
Alan--
If it was easy, anyone could do it.

Top
#64466 - 04/08/06 04:21 PM Re: Tie handles
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
GTE

 Quote:
When are tie handles between single pole circuit breakers not approved?


I want to be sure we know what your asking.

Dave T gave a good answer if the question is 'When can a handle tie be used?'

However I was wondering if your question is 'What is an approved handle tie?'

Alan

210.4(B) 2002
 Quote:
210.4(B) Dwelling Units. In dwelling units, a multiwire branch circuit supplying more than one device or equipment on the same yoke shall be provided with a means to disconnect simultaneously all ungrounded conductors at the panelboard where the branch circuit originated.


All that section requires is a 'means to disconnect simultaneously all ungrounded conductors at the panelboard'.

Here is a handbook image which shows it much better than I could draw it.



IMO the handbook image is directly supported by the text of 210.4(B)



[This message has been edited by iwire (edited 04-08-2006).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#64467 - 04/08/06 07:40 PM Re: Tie handles
jfwayer Offline
Member

Registered: 05/15/05
Posts: 30
Loc: Fairmont, WV, USA
Handle ties are also used to meet the 6 disconnecting means rule:

NEC 2005:

230.71 Maximum Number of Disconnects.
(A) General. The service disconnecting means for each service permitted by 230.2, or for each set of service-entrance conductors permitted by 230.40, Exception Nos. 1, 3, 4, or 5, shall consist of not more than six switches or sets of circuit breakers, or a combination of not more than six switches and sets of circuit breakers, mounted in a single enclosure, in a group of separate enclosures, or in or on a switchboard. There shall be not more than six sets of disconnects per service grouped in any one location. For the purpose of this section, disconnecting means used solely for power monitoring equipment, transient voltage surge suppressors, or the control circuit of the ground-fault protection system or power-operable service disconnecting means, installed as part of the listed equipment, shall not be considered a service disconnecting means.
(B) Single-Pole Units. Two or three single-pole switches or breakers, capable of individual operation, shall be permitted on multiwire circuits, one pole for each ungrounded conductor, as one multipole disconnect, provided they are equipped with handle ties or a master handle to disconnect all conductors of the service with no more than six operations of the hand.

fixed speling

[This message has been edited by jfwayer (edited 04-08-2006).]
_________________________
JFW

Top
#64468 - 04/08/06 09:02 PM Re: Tie handles
GTE Offline
Member

Registered: 03/26/03
Posts: 48
Loc: Bridgehampton, N.Y. USA
Iwire.
What I wanted to know is when do have to use a 2-pole breaker or when tie handles are not allowed?

Top
#64469 - 04/08/06 09:32 PM Re: Tie handles
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
The answer has been given, although maybe not clearly.

If the situation requires a simultaneous disconnect, as in manual operation, a handle tie is adequate. In fact, the disconnect need not be a breaker.

However, if simultaneous over-current protection is required, then a 2- or 3-pole breaker must be used. The handle tie is not what makes all handles trip.

If you want every situation that requires one over the other spelled out, I don't think we'll be doing that here. Maybe you can tell us your specific situation.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com

Top
#64470 - 04/09/06 04:32 AM Re: Tie handles
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
 Quote:
Iwire.
What I wanted to know is when do have to use a 2-pole breaker or when tie handles are not allowed?


OK I think I can help out.

 Quote:
240.20 Ungrounded Conductors.
(A) Overcurrent Device Required.


A fuse or an overcurrent trip unit of a circuit breaker shall be connected in series with each ungrounded conductor. A combination of a current transformer and overcurrent relay shall be considered equivalent to an overcurrent trip unit.
FPN:For motor circuits, see Parts III, IV, V, and X of Article 430.

(B) Circuit Breaker as Overcurrent Device. Circuit breakers shall open all ungrounded conductors of the circuit unless otherwise permitted in 240.20(B)(1), (B)(2), and (B)(3).

(1) Multiwire Branch Circuit. Except where limited by 210.4(B), individual single-pole circuit breakers, with or without approved handle ties, shall be permitted as the protection for each ungrounded conductor of multiwire branch circuits that serve only single-phase line-to-neutral loads.

(2) Grounded Single-Phase and 3-wire dc Circuits. In grounded systems, individual single-pole circuit breakers with approved handle ties shall be permitted as the protection for each ungrounded conductor for line-to-line connected loads for single-phase circuits or 3-wire, direct-current circuits.

(3) 3-Phase and 2-Phase Systems. For line-to-line loads in 4-wire, 3-phase systems or 5-wire, 2-phase systems having a grounded neutral and no conductor operating at a voltage greater than permitted in 210.6, individual single-pole circuit breakers with approved handle ties shall be permitted as the protection for each ungrounded conductor.



Examples of circuits in which approved handle ties are permitted according to 240.20(B)(2) or 240.20(B)(3).

It is interesting to note that we can use handle ties on loads such as dryers and ranges.

I think most of us assume a common trip breaker is required.




[This message has been edited by iwire (edited 04-09-2006).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#64471 - 04/10/06 11:54 PM Re: Tie handles
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
Original question...
"When are tie handles between single pole circuit breakers not approved?"

When the "handle tie" is a nail, wire or other garbage someone dropped in the holes in the handles.

An approved one, would be one made for the purpose by the manufacturer for that type of breaker.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top