ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Page 1 of 4 1 2 3 4 >
Topic Options
Rate This Topic
#64363 - 04/06/06 09:08 AM New Transformers/New Short Circuit Current
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
In an existing building the utility is replacing transformers (for an addition which will have a new separate main disconnect). The new transformers have a much higher short circuit let through current. The original building service is a 50 year old ITE switchboard.
The let through current is over 80,000A.
The short circuit rating of the main circuit braker is 50,000A. (the transformers are about ten feet away from the switchboard indoors in a room next to the electric service room)
Any suggestions (other than replacing the entire switchboard)??? The main circuit breaker and switchboard are rated at 1600A.
Top
Work Gear for Electricians and the Trades
#64364 - 04/06/06 02:33 PM Re: New Transformers/New Short Circuit Current
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
http://www.ferrazshawmut.com/products/pdf_107/A4BQ.pdf

try current limiting fuses in a appropriate enclosure between the transformer and the main.
_________________________
Earl
Top
#64365 - 04/06/06 05:25 PM Re: New Transformers/New Short Circuit Current
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
Anything put between the transformer and the existing equipment would have to have a tested series rating. It is all but impossible to get a calculated series rating unless the existing equipment are "power circuit breakers".

Have you thought about running the incoming cables around the building a few times? This will add impedance and lower the available fault current.
Top
#64366 - 04/06/06 05:43 PM Re: New Transformers/New Short Circuit Current
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
You only have a few choices. By mearly adding a current limiting device between the transformer and the 50kAIC breaker doesn't help. They must be series rated together, which they generally are not for older equipment.
You can add a reactor downstream of the transformer, and it will limit fault current, but be careful of voltage drop problems.
Validate the fault current that you are being told, at least with an infinite primary calculation, and don't forget to add contribution from downstream motors.
Wire can reduce current significantly, so run lots of wire as mentioned by JBD.
_________________________
Ron
Top
#64367 - 04/06/06 06:11 PM Re: New Transformers/New Short Circuit Current
SolarPowered Offline
Member
Registered: 07/05/04
Posts: 625
Loc: Palo Alto, CA, USA
Tie the wire in a knot.
Top
#64368 - 04/06/06 06:16 PM Re: New Transformers/New Short Circuit Current
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
Is the transformer something close to 3750kVA with a 480V secondary?
_________________________
Ron
Top
#64369 - 04/06/06 08:42 PM Re: New Transformers/New Short Circuit Current
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
The Circuit Breaker can be the first or second element in series....

Install L or T type current limiting fuses with an appropriate rating: have an EE design it.

If the bussing permits, install a different breaker.

With such an old piece of gear: scrap it.... (I can't believe that old breaker is still passing its tests.)

Alternately, feed the existing service from the new installation. Re-engineer it.

Blame the extra on the Poco. Not your fault.
_________________________
Tesla
Top
#64370 - 04/07/06 04:22 AM Re: New Transformers/New Short Circuit Current
winnie Offline
Member
Registered: 09/15/03
Posts: 649
Loc: boston, ma
Perhaps you could just run each phase in its own conduit.... (*ducking*)

-Jon
Top
#64371 - 04/07/06 05:10 AM Re: New Transformers/New Short Circuit Current
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
Jon,
That would help, but be sure that PVC conduit is used.
_________________________
Ron
Top
#64372 - 04/07/06 08:52 AM Re: New Transformers/New Short Circuit Current
Bob Offline
Member
Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
Check the fault current as given. If you were given a fault current with an infinite source the actual value will be less. You will need to recaculate the fault including the utiltiy system impedance. The utility may be reluctant to give this information.
Top
Page 1 of 4 1 2 3 4 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 50 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals