#64301 - 04/05/06 02:58 PM What is the equivalent DC current...?
Cinner Offline
Member
Registered: 12/01/04
Posts: 78
Loc: Kelowna, B.C., Canada
What is the DC current value that will give you the same amount of heat as 1.0 amp rms going through a 10 ohm resistor?

A).637 a
b) .707 a
c) 1.0 a
d) 1.41 a



[This message has been edited by Cinner (edited 04-05-2006).]
Top
Work Gear for Electricians and the Trades
#64302 - 04/05/06 03:06 PM Re: What is the equivalent DC current...?
NJwirenut Offline
Member
Registered: 09/15/01
Posts: 806
Loc: Bergen County, NJ
C--1 ampere
Top
#64303 - 04/05/06 03:26 PM Re: What is the equivalent DC current...?
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Actually it is (b).707

Roger
Top
#64304 - 04/05/06 04:04 PM Re: What is the equivalent DC current...?
JoeTestingEngr Offline
Member
Registered: 11/04/05
Posts: 781
Loc: Chicago, Il.
I agree with NJ. If you multiply the RMS by .707 again, it becomes PMS, which should be avoided.
Joe
Top
#64305 - 04/05/06 04:21 PM Re: What is the equivalent DC current...?
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Oooooops, I read the question again

I also agree with NJ

Roger
Top
#64306 - 04/05/06 04:25 PM Re: What is the equivalent DC current...?
Cinner Offline
Member
Registered: 12/01/04
Posts: 78
Loc: Kelowna, B.C., Canada
Shouldn't the answer be:

1/0.707 = 1.41

1.41 x .637 = 0.9 amps.

Do you agree?
Top
#64307 - 04/05/06 04:38 PM Re: What is the equivalent DC current...?
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Cinner, the "rms" (which I somehow read as "AC" when I first read the question, who knows where my reading skills jaunted off to) already has the AC value equal to the DC value.

Roger
Top
#64308 - 04/05/06 05:30 PM Re: What is the equivalent DC current...?
JoeTestingEngr Offline
Member
Registered: 11/04/05
Posts: 781
Loc: Chicago, Il.
Cinner,
A few years ago, meters started coming out with the "True RMS" labels all over them. These meters give you a reading that is already the peak value X .707, or the RMS, or the heating value. If you had a less spiffy, average reading meter, you would take the displayed "average" value / .637, to get to peak, and then X .707 to get to your RMS value. Hope this helps.
Joe
But still avoid the PMS.

[This message has been edited by JoeTestingEngr (edited 04-05-2006).]
Top
#64309 - 04/06/06 06:13 AM Re: What is the equivalent DC current...?
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
And the 10-ohm figure specified is one of these pieces of data thrown in to a question which is of no significance.

Since P = I^2 x R, 1 amp DC will give the same amount of heat as 1 amp RMS AC no matter what the resistance value (so long as it's the same in both cases, of course).
Top
#64310 - 04/06/06 12:28 PM Re: What is the equivalent DC current...?
RODALCO Offline
Member
Registered: 12/08/05
Posts: 854
Loc: Titirangi, Akld, New Zealand
Answer C, 1 Amp.
_________________________
The product of rotation, excitation and flux produces electricty.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals