#64290 - 04/04/06 12:30 PM two soda machines  
ShockMe77  Offline
Member
Joined: Jun 2005
Posts: 821
Rahway, New Jersey
Was curious to know if (2) soda machines set in the middle of a room could be wired with flexible cord attached to a twist-lock receptacle attached to the ceiling grid of a suspended ceiling. Would 400.7 (A)(6) cover me?


Work Gear for Electricians and the Trades

#64291 - 04/04/06 12:51 PM Re: two soda machines  
raider1  Offline
Member
Joined: Jul 2005
Posts: 46
north logan, utah, US
Also take a look at 422.16(A)

Chris


#64292 - 04/04/06 01:35 PM Re: two soda machines  
gfretwell  Online Content


Member
Joined: Jul 2004
Posts: 9,058
Estero,Fl,usa
They may want some independent support of the box. Running an extra support wire or two should calm that fear.


Greg Fretwell

#64293 - 04/05/06 01:50 PM Re: two soda machines  
Geno  Offline
Member
Joined: Aug 2001
Posts: 16
Syracuse, NY USA
look at 422.51


#64294 - 04/05/06 05:40 PM Re: two soda machines  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,802
Brick, NJ USA
Shock:
'Cord' cannot be used for permanent wiring methods. That said, IF you have a vend with a cord long enough to reach your receptacle, no problem.

IF you are proposing a twistlock to cord to a 1900 box that the machine cord will plug into; that does not fly.

Dependent on the ceiling height, you may want to consider a power pole, or IMC/RGC from ceiling to floor with the recept(s) installed therein.

John


John

#64295 - 04/05/06 07:18 PM Re: two soda machines  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
By the way vending machines require GFCI protection if integral or by the branch circuit.

2005 - 422.51


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#64296 - 04/05/06 07:56 PM Re: two soda machines  
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
Hotline1:

Wouldn't a permanently installed cord hanging from a box to a female cord cap be explicitly permitted by 400.7(A)(1)?

-Jon


#64297 - 04/05/06 08:59 PM Re: two soda machines  
gfretwell  Online Content


Member
Joined: Jul 2004
Posts: 9,058
Estero,Fl,usa
Perhaps I missed what he was trying to do. I was thinking the receptacle was in a box, attached to the grid and it was connected with an article 300 wiring method above the ceiling (MC whip or something).


Greg Fretwell


Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.7900 MB (Peak: 0.9500 MB) Zlib enabled. Server Time: 2017-03-27 04:47:34 UTC