Was curious to know if (2) soda machines set in the middle of a room could be wired with flexible cord attached to a twist-lock receptacle attached to the ceiling grid of a suspended ceiling. Would 400.7 (A)(6) cover me?
Top
Work Gear for Electricians and the Trades
#64291 - 04/04/06 09:51 AM Re: two soda machines
raider1 Offline
Member
Registered: 07/08/05
Posts: 46
Loc: north logan, utah, US
Also take a look at 422.16(A)

Chris
Top
#64292 - 04/04/06 10:35 AM Re: two soda machines
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
They may want some independent support of the box. Running an extra support wire or two should calm that fear.
_________________________
Greg Fretwell
Top
#64293 - 04/05/06 10:50 AM Re: two soda machines
Geno Offline
Member
Registered: 08/27/01
Posts: 16
Loc: Syracuse, NY USA
look at 422.51
Top
#64294 - 04/05/06 02:40 PM Re: two soda machines
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Shock:
'Cord' cannot be used for permanent wiring methods. That said, IF you have a vend with a cord long enough to reach your receptacle, no problem.

IF you are proposing a twistlock to cord to a 1900 box that the machine cord will plug into; that does not fly.

Dependent on the ceiling height, you may want to consider a power pole, or IMC/RGC from ceiling to floor with the recept(s) installed therein.

John
_________________________
John
Top
#64295 - 04/05/06 04:18 PM Re: two soda machines
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
By the way vending machines require GFCI protection if integral or by the branch circuit.

2005 - 422.51
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#64296 - 04/05/06 04:56 PM Re: two soda machines
winnie Offline
Member
Registered: 09/15/03
Posts: 649
Loc: boston, ma
Hotline1:

Wouldn't a permanently installed cord hanging from a box to a female cord cap be explicitly permitted by 400.7(A)(1)?

-Jon
Top
#64297 - 04/05/06 05:59 PM Re: two soda machines
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Perhaps I missed what he was trying to do. I was thinking the receptacle was in a box, attached to the grid and it was connected with an article 300 wiring method above the ceiling (MC whip or something).
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 30 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals