The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Members: Non-Members: Did you know?
by Admin
Today at 02:34 PM
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 36
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
1 registered (Admin), 83 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#64204 - 04/02/06 10:31 AM Understanding nameplate information.
Cinner Offline
Member
Registered: 12/01/04
Posts: 77
Loc: Kelowna, B.C., Canada
Can someone explain a couple of things to me on this nameplate info for a convection oven:

TOTAL KW = 5.5KW

208, 240v 3 Phase Loading - KW per Phase:
L1-L2 = 2.5, L2-L3 = 0 , L1-L3 = 3Kw

Nominal Amps per line wire:
3 Phase 208 Volt
L1 =23, L2= 10, L3=12

Why is there unbalanced loads per phase and how would you choose a cable wire size with all the different amperages? Would you base cable wire size on the largest - 23 amps? Would you use a 3 pole 30 amp breaker?
Top
Work Gear for Electricians and the Trades
#64205 - 04/02/06 10:39 AM Re: Understanding nameplate information.
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
The unbalanced current is the result of single phase fan motors and controls.

Yes you must select a cord and branch circuit with at least a 23 amp capacity.

[This message has been edited by iwire (edited 04-02-2006).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#64206 - 04/02/06 10:43 AM Re: Understanding nameplate information.
Cinner Offline
Member
Registered: 12/01/04
Posts: 77
Loc: Kelowna, B.C., Canada
L2-L3 = 0 kw...why no load b/w 2 and 3?

[This message has been edited by Cinner (edited 04-02-2006).]
Top
#64207 - 04/02/06 12:35 PM Re: Understanding nameplate information.
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
With no load between L2-L3 it would be very easy to convert the oven to work on a 2 wire single phase supply.
Top
#64208 - 04/02/06 10:26 PM Re: Understanding nameplate information.
Cinner Offline
Member
Registered: 12/01/04
Posts: 77
Loc: Kelowna, B.C., Canada
would a 3 pole 30 amp breaker be sufficient?