The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
1 registered (LongRunner), 206 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#64204 - 04/02/06 10:31 AM Understanding nameplate information.
Cinner Offline
Member

Registered: 12/01/04
Posts: 77
Loc: Kelowna, B.C., Canada
Can someone explain a couple of things to me on this nameplate info for a convection oven:

TOTAL KW = 5.5KW

208, 240v 3 Phase Loading - KW per Phase:
L1-L2 = 2.5, L2-L3 = 0 , L1-L3 = 3Kw

Nominal Amps per line wire:
3 Phase 208 Volt
L1 =23, L2= 10, L3=12

Why is there unbalanced loads per phase and how would you choose a cable wire size with all the different amperages? Would you base cable wire size on the largest - 23 amps? Would you use a 3 pole 30 amp breaker?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#64205 - 04/02/06 10:39 AM Re: Understanding nameplate information.
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
The unbalanced current is the result of single phase fan motors and controls.

Yes you must select a cord and branch circuit with at least a 23 amp capacity.

[This message has been edited by iwire (edited 04-02-2006).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#64206 - 04/02/06 10:43 AM Re: Understanding nameplate information.
Cinner Offline
Member

Registered: 12/01/04
Posts: 77
Loc: Kelowna, B.C., Canada
L2-L3 = 0 kw...why no load b/w 2 and 3?

[This message has been edited by Cinner (edited 04-02-2006).]

Top
#64207 - 04/02/06 12:35 PM Re: Understanding nameplate information.
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
With no load between L2-L3 it would be very easy to convert the oven to work on a 2 wire single phase supply.

Top
#64208 - 04/02/06 10:26 PM Re: Understanding nameplate information.
Cinner Offline
Member

Registered: 12/01/04
Posts: 77
Loc: Kelowna, B.C., Canada
would a 3 pole 30 amp breaker be sufficient?