#64146 - 03/31/06 01:28 PM A I C rating charts
drgnz23 Offline
Member
Registered: 02/17/02
Posts: 56
Loc: los angeles
Has anybody heard of this ? Arc interupting current chart for breakers.
Top
Work Gear for Electricians and the Trades
#64147 - 03/31/06 01:59 PM Re: A I C rating charts
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
You'll have to explain a bit more. AIC ratings are the amp interrupting current that is part of every circuit breaker or fuse assembly. They start around 10,000AIC and go up to 200,000 AIC.
_________________________
Ron
Top
#64148 - 04/04/06 04:16 PM Re: A I C rating charts
drgnz23 Offline
Member
Registered: 02/17/02
Posts: 56
Loc: los angeles
Im sorry i wasnt specific . My boss needs to figured out how to find the arc fault rating for a breaker. Is there some sort of formula?
Top
#64149 - 04/04/06 04:40 PM Re: A I C rating charts
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
I'm not sure what you mean by arc fault rating. If you mean amps interupting capacity, you would find that information molded into the case of the breaker or printed on a small sticker attached to the breaker. If there are no markings, the AIC is 5000 amps. If you don't have the breaker in question on hand, the information is usually available in the manufacturers catalog.
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#64150 - 04/05/06 02:45 PM Re: A I C rating charts
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
AIC requirements are requested/required by most AHJ's.

AIC formulas are to involved to include here, but try the Bussman website. They should have the info either as downloadable, or you could request the booklet.

It's math, not to deep, and their method is acceptable.

AIC ratings of various CB's are available from the mfg; there is a lot of useful info within most catalogs, trip curves, etc.

John
_________________________
John
Top
#64151 - 04/05/06 06:37 PM Re: A I C rating charts
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
AIC ratings (which apply to protective devices)are determined through testing by an NRTL.

SCCR (short circuit current rating) for panels my be determined by testing or design.

SCA (short circuit amps) may be calculated for various points in an electrical system.

Arc flash incident energy values may be calculated by knowing the SCA at a specific point and the time current charecteristics of the overcurrent device protecting that point.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals