The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
1 registered (gfretwell), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#64146 - 03/31/06 01:28 PM A I C rating charts
drgnz23 Offline
Member

Registered: 02/17/02
Posts: 56
Loc: los angeles
Has anybody heard of this ? Arc interupting current chart for breakers.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#64147 - 03/31/06 01:59 PM Re: A I C rating charts
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
You'll have to explain a bit more. AIC ratings are the amp interrupting current that is part of every circuit breaker or fuse assembly. They start around 10,000AIC and go up to 200,000 AIC.
_________________________
Ron

Top
#64148 - 04/04/06 04:16 PM Re: A I C rating charts
drgnz23 Offline
Member

Registered: 02/17/02
Posts: 56
Loc: los angeles
Im sorry i wasnt specific . My boss needs to figured out how to find the arc fault rating for a breaker. Is there some sort of formula?

Top
#64149 - 04/04/06 04:40 PM Re: A I C rating charts
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
I'm not sure what you mean by arc fault rating. If you mean amps interupting capacity, you would find that information molded into the case of the breaker or printed on a small sticker attached to the breaker. If there are no markings, the AIC is 5000 amps. If you don't have the breaker in question on hand, the information is usually available in the manufacturers catalog.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#64150 - 04/05/06 02:45 PM Re: A I C rating charts
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
AIC requirements are requested/required by most AHJ's.

AIC formulas are to involved to include here, but try the Bussman website. They should have the info either as downloadable, or you could request the booklet.

It's math, not to deep, and their method is acceptable.

AIC ratings of various CB's are available from the mfg; there is a lot of useful info within most catalogs, trip curves, etc.

John
_________________________
John

Top
#64151 - 04/05/06 06:37 PM Re: A I C rating charts
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
AIC ratings (which apply to protective devices)are determined through testing by an NRTL.

SCCR (short circuit current rating) for panels my be determined by testing or design.

SCA (short circuit amps) may be calculated for various points in an electrical system.

Arc flash incident energy values may be calculated by knowing the SCA at a specific point and the time current charecteristics of the overcurrent device protecting that point.