The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
0 registered (), 172 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#64053 - 03/29/06 07:02 PM Need more room in Panel...
Cinner Offline

Registered: 12/01/04
Posts: 77
Loc: Kelowna, B.C., Canada
Does anyone know of a Square D type circuit breaker that is a side by side?....basically letting you put 2 of 15 amp breakers where usually only 1 is placed. Are they called a particular name?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#64054 - 03/29/06 07:18 PM Re: Need more room in Panel...
BigB Offline

Registered: 03/31/04
Posts: 725
Loc: Tucson, AZ USA
Homeline or QO? New Homeline twins are available. As far as QO, I've seen some old twins that are side by side rather than stacked, don't know if they are still made. Maybe someone else will chime in.

#64055 - 03/29/06 07:27 PM Re: Need more room in Panel...
mahlere Offline

Registered: 11/17/05
Posts: 514
Loc: New Jersey
they make QO tandems as well. I don't know if they are available in canada or not.

#64056 - 03/29/06 07:55 PM Re: Need more room in Panel...
Sixer Offline

Registered: 08/08/05
Posts: 264
Loc: Canada
Yes, the QO tandems are available in Canada.

"Will it be cheaper if I drill the holes for you?"

#64057 - 03/29/06 08:00 PM Re: Need more room in Panel...
SolarPowered Offline

Registered: 07/05/04
Posts: 615
Loc: Palo Alto, CA, USA
QO tandems can be had in both Class CTL and non-Class CTL versions. They aren't side-by-side, though--they're in a tandem arrangement.

#64058 - 03/29/06 08:22 PM Re: Need more room in Panel...
macmikeman Offline

Registered: 07/16/02
Posts: 718
Loc: Honolulu, Hawaii
I saw a tandem 14 sq-d in a bolt on panel in a resturant the other day. I was a bit suprised. I have never seen tandems in a bolt on before. Is this common? Or did somebody jury rig here. I didn't remove the panel cover, as I was there to look at something else.

#64059 - 03/29/06 08:58 PM Re: Need more room in Panel...
caselec Offline

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
Square D Panelboards accept both QOB (bolt on) and QO (plug on) breakers. I have been told that they recommend using QO breakers instead of QOB when adding additional breakers in the field. I can pretty much guarantee that the panelboard was not listed for tandem breakers and I’m sure the breaker used was clearly marked non-CTL for replacement use only.

BigB, what new Homline tandem breakers are you referring to? HOMT breakers in 15 and 20 amp have been available since the beginning of Homeline. They later added the larger quad breakers (30-50).

Curt Swartz

#64060 - 03/30/06 08:06 AM Re: Need more room in Panel...
luckyshadow Offline

Registered: 01/04/05
Posts: 305
Loc: Maryland USA
Here in the US - Home depot does carry qo tandum breakers that are the side by side set up. They two different types for both QO panels and CH.
I'm not sure about Canada though.

#64061 - 03/30/06 09:00 AM Re: Need more room in Panel...
Roger Offline

Registered: 05/18/02
Posts: 1779
Loc: N.C.
There are even Quad breakers in Homeline. See the links below for info on Homeline and QO lines.


#64062 - 03/30/06 10:25 AM Re: Need more room in Panel...
JBD Offline

Registered: 07/12/01
Posts: 599
Loc: WI, USA
The old Square D tandem breakers were front-to-back. The tandems since the 80's have been side-by-side. The new design gives the 2 pole devices the appearance of a quad breaker, but it is really (1) 2pole + (2) 1poles.

All UL Listed panels built since the 60's are CTL. So non-CTL breakers should only be installed in panels that are over 40 years old that have wiring diagrams showing which spaces are designed for tandem circuits.

My personal belief is that non-CTL tandem breakers should go the way of the old delta breakers.