ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Page 1 of 5 1 2 3 4 5 >
Topic Options
Rate This Topic
#63690 - 03/23/06 08:46 PM 2- 30amp receps
drgnz23 Offline
Member
Registered: 02/17/02
Posts: 56
Loc: los angeles
i was just reading another topic from another forum about having 2 30a 220v receptacles on one circuit (welder and compressor) on one 30 amp breaker.(not being used at the same time0).Is this a safe practice? To my knowledge this shouldnt be done regardless if you dont operate at the same time....what do you think?
Top
Work Gear for Electricians and the Trades
#63691 - 03/23/06 10:08 PM Re: 2- 30amp receps
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
Why not?
I don't know of anything that says you can't have 2 receptacle outlets on a 30a circuit.
_________________________
Greg Fretwell
Top
#63692 - 03/24/06 12:12 AM Re: 2- 30amp receps
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Depends on the load.... 210.21+210.23

And no, over-all I don't think it a safe or wise practice. There is no guarantee of only one in use at a time. One device cycles automaticaly, the other is a welder. See 630... Although a welder is intermitant, and it is allowed to have multiple welders on the same circuit the OCP and wire size rules are expanded, and differ slightly from a normal branch circuit.

Without knowing the data plates and circuit particulars, I would say, no.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#63693 - 03/24/06 12:28 AM Re: 2- 30amp receps
macmikeman Offline
Member
Registered: 07/16/02
Posts: 717
Loc: Honolulu, Hawaii
Double pole - double throw switch?
Top
#63694 - 03/24/06 01:35 AM Re: 2- 30amp receps
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
All of us install multiple receptacle outlets on 15 and 20 amp circuits all the time with no idea at all what will be plugged into them.

Why would this practice suddenly become unsafe once we move to 30 amp circuits?

Article 630 gives us some options for saving money when supplying welders but we do not have to use those options, we can supply a welder with a 30 amp cord cap with a 'standard' 30 amp branch circuit.

I see no NEC reason not to do this, it in my opinion is a design choice.

If the person paying the bill tells me they are fine with one circuit I would have no problem supplying them with one circuit once I explained the circuit may trip if both units operate at the same time.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#63695 - 03/24/06 04:28 AM Re: 2- 30amp receps
PCBelarge Offline
Member
Registered: 06/08/03
Posts: 681
Loc: Dobbs Ferry, NY, USA
I agree with Bob.
If both units are used at the same time... the circuit breaker will open...exactly what the NEC wants to happen... but the customer, if not warned will not be too happy.
_________________________
Pierre Belarge
Top
#63696 - 03/24/06 07:26 AM Re: 2- 30amp receps
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Assuming the nameplates require similar circuits, I see no problem.

BUT- that's a big assumption. The two appliances are treated quite differently as to wire sizing and over-current protection; Just because they have the same plug is no guarantee. Nevertheless, in Harry Homowners' garage, where Harry is going to putz around solo, it ought to work out OK.
Change that to a guy trying to run a business in his garage....and my answer will change.
Top
#63697 - 03/24/06 09:38 AM Re: 2- 30amp receps
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
I am fixin' to do exactly the same thing with my welder and a new pressure cleaner I just ordered. In a practical sense I know I could unplug one and plug in the other but I am going to install another receptacle.
_________________________
Greg Fretwell
Top
#63698 - 03/24/06 10:50 AM Re: 2- 30amp receps
ghost307 Offline
Member
Registered: 05/09/05
Posts: 899
Loc: Chicago Illinois USA
I did the same thing at a big honkin' laboratory complex a few years ago. Each lab had a piece of equipment that the staff would roll to different places in the lab based on their particular research project. There were 3 possible locations, but each lab only had 1 machine...1 circuit, 3 receptacles.
Worked great.
No problems...Code or otherwise.
_________________________
Ghost307
Top
#63699 - 03/24/06 11:51 AM Re: 2- 30amp receps
Texas_Ranger Offline
Member
Registered: 12/17/01
Posts: 2391
Loc: Vienna, Austria
Please tell an innocent European why two appliances with the same voltage and amp draw would need different wire? I assume with some loads you could downsize some for cycling, but generally 30 amps are 30 amps, right?
Trip characteristics are a different piece of cake of course.

I think mainly it's a design thing - we usually put our CEE receptacles on dedicated circuits, so they can be loaded to their full ampacity.
Top
Page 1 of 5 1 2 3 4 5 >

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 121 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals