#63495 - 03/18/06 05:33 PM nuissance fire alarm sounding
sandro2 Offline
Member
Registered: 03/26/05
Posts: 49
Loc: philadelphia,PA
I got a call about a fire alarm system constantly sounding. There is nothing that indicates an actual alarm unless they are resetting it. The apt. building is unoccupied.
The system was installed 10yrs ago.
It is a Firelite 4 zone panel.
What could be some causes?
Top
Work Gear for Electricians and the Trades
#63496 - 03/18/06 06:45 PM Re: nuissance fire alarm sounding
luckyshadow Offline
Member
Registered: 01/04/05
Posts: 305
Loc: Maryland USA
I once had water flow alarms that turned out to air bubbles in the system.
dust in a smoke will cause false alarms.
You will need to know if the panel is being reset thus cleared of what zone the trouble is on. Chasing a ghost in a F/A can be "fun"
Is it an addressable system ? If so the panel will tell you what device set it off.
Keep us posted on this
Top
#63497 - 03/19/06 01:38 PM Re: nuissance fire alarm sounding
hypress Offline
Member
Registered: 07/20/04
Posts: 129
Loc: Charleston WV
Look for roaches in the smoke detectors. If the building is unoccupied there could be some unwanted guests. I have worked in some lowcost houseing projects and found roaches in detectors. A good indication is that it is always the same zone or zones.
Top
#63498 - 03/19/06 07:10 PM Re: nuissance fire alarm sounding
mxslick Offline
Member
Registered: 10/24/04
Posts: 803
Loc: Atomic City, ID USA
Watch out for rodents chewing on wires or doing thier business on devices, that'll do it too...
_________________________
Stupid should be painful.
Top
#63499 - 03/19/06 08:06 PM Re: nuissance fire alarm sounding
sandro2 Offline
Member
Registered: 03/26/05
Posts: 49
Loc: philadelphia,PA
I guess that is why the owner asked me if rodents could be the cause.
Top
#63500 - 03/20/06 09:32 AM Re: nuissance fire alarm sounding
CTwireman Offline
Member
Registered: 02/07/02
Posts: 840
Loc: Connecticut, USA
Another problem could be a roof leak causing a device to short, or excessive humidity could be causing a smoke detector to trip. I've seen both cause a nuisance alarm.

Peter
_________________________
Peter
Top
#63501 - 03/20/06 07:45 PM Re: nuissance fire alarm sounding
JoeTestingEngr Offline
Member
Registered: 11/04/05
Posts: 781
Loc: Chicago, Il.
I've had several locations where construction dust or moisture have caused photoelectrics to go into alarm. These should latch the zone though. Many times I'm told that the fire alarm is going off when it is really the trouble audible, which doesn't need acknowleged to clear in many systems.
Joe
Top
#63502 - 03/21/06 12:33 AM Re: nuissance fire alarm sounding
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Assuming this is a non-addressable system?

Unnoccupied building? Wafting dust bunnies? What kind of general condition is it in? Intermitant power and dead back-up batteries?

A good place to start would be tech support....

Otherwise, I think DUST.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#63503 - 03/21/06 10:21 AM Re: nuissance fire alarm sounding
CTwireman Offline
Member
Registered: 02/07/02
Posts: 840
Loc: Connecticut, USA
Most manufacturers recommend that smoke detectors be replaced every 10 years.

Peter

[This message has been edited by CTwireman (edited 03-21-2006).]
_________________________
Peter
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals