I know you cannot install counter top receptacles face up, but what about 4000 wire mold. I have an architect that wants me to place wire mold on the ground face up. I do not think this is ok, but I do not have any code article to back it up. Any help will be welcomed.
Top
Work Gear for Electricians and the Trades
#63478 - 03/18/06 06:53 AM Re: Face up Wiremold
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
Sparks:
Can't seem to put a NEC Reference to exactly what you asked

You said "on the ground" ??

To bad 'common sense' isn't in the NEC!

I'll delve into this over the weekend for a NEC ref, if there is one.

John
_________________________
John
Top
#63479 - 03/18/06 07:04 AM Re: Face up Wiremold
earlydean Offline
Member
Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
Looking at the UL white book, I see no info either way. Looking at the wiremold installation instructions I see no direction either, although the illustrations show base pieces being mounted both horizontally and vertically (but not the receptacles - they are always horizontal in the pictures)
I would venture my opinion that mounting wiremold 4000 receptacles face-up on the ground should be permitted in some instances, but may not be such a good idea in all locations. The NEC requires all installations to be "acceptable to the AHJ" and to be "suitable for the conditions of use".(110.2 & .3)
It would be my recommendation, then, that prior to installation, you contact your AHJ for their acceptance of the plan.
_________________________
Earl
Top
#63480 - 03/18/06 08:03 AM Re: Face up Wiremold
Gregtaylor Offline
Member
Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
Is this a residential app? Receptacles within 12" of a wall that are taking the place of flush receptacles, perhaps because the wall is glass may be face up and are not required to be covered. This would depend of course on the manufacturers specs, but the code would allow it.
Top
#63481 - 03/18/06 08:16 AM Re: Face up Wiremold
macmikeman Offline
Member
Registered: 07/16/02
Posts: 718
Loc: Honolulu, Hawaii
I would check the listing for wiremold. I have doubts about it having a listing for floor receptacle use.
Top
#63482 - 03/18/06 12:13 PM Re: Face up Wiremold
luckyshadow Offline
Member
Registered: 01/04/05
Posts: 305
Loc: Maryland USA
Without getting too deep into the code- Everything I read pertaining to surface metal raceways and the like , uses not permitted: where subject to severe physical damage.
I would think mounting 4000 wiremold on the floor , face up would be subject to severe physical damage. Such damage coming from mops and water , vacuum cleaners, furniture, and peoples feet. Someone WILL stand on it!
Top
#63483 - 03/18/06 10:46 PM Re: Face up Wiremold
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
Thanks for the replys. This will be going into a computer room for elementry school kids under the desk. Monday I will be talking to the AHJ. I do not want to mount it this way. I was looking for some hard copy stuff to show the GC just for proof. Thanks again.Sam
Top
#63484 - 03/19/06 03:59 AM Re: Face up Wiremold
e57 Offline
Member
Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
I agree with lucky.

386.12 Uses Not Permitted.
Surface metal raceways shall not be used in the following:
(1) Where subject to severe physical damage, unless otherwise approved

If all else fails push the inspector over it so he trips.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#63485 - 03/19/06 04:31 AM Re: Face up Wiremold
jfwayer Offline
Member
Registered: 05/15/05
Posts: 30
Loc: Fairmont, WV, USA
You would find it hard to damage wiremold 4000 without a hammer. It's made of .050" galvanized steel.
_________________________
JFW
Top
#63486 - 03/19/06 04:49 AM Re: Face up Wiremold
electure Offline


Member
Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
Before you start pushing the inspector around so that he sees the face up recps, consider this:




Taken directly from w-mold's catalogue
1500/2600 series. I don't think they've got an issue with the plug facing up.

Don't put your foot in your mouth
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
0 registered (), 76 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals