#63031 - 03/04/06 03:58 PM Underground fault
normel Offline
Junior Member
Registered: 10/22/04
Posts: 9
Need help in troubleshooting the following: Outdoor circuit from GCI receptacle to light switch (for pool light), on to two receptacles, all wiring between each is buried 12/2 w/g UF. When powered up, GFCI trips but after 15 sec to 5 minutes. I have isolated the fault to the wires between the switch and receptacle, but am perplexed as to why the delay in tripping the GFCI. Would a nick in the neutral insulation be causing this?
Top
Work Gear for Electricians and the Trades
#63032 - 03/04/06 06:46 PM Re: Underground fault
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
That, or leakage from the lights. The delay could, in part, be related to temperatuse changes...or a 'borderline' fault that is very close to the trip level of the GFI.

I think it's time to get a megger and do some serious testing.
Top
#63033 - 03/04/06 06:53 PM Re: Underground fault
normel Offline
Junior Member
Registered: 10/22/04
Posts: 9
It's not the lights. It will still trip with them out of the circuit. The suspect length of wire will trip the GFCI with nothing connected to the end. A nick is what I suspect, but am surprised by the variable times on the GFCI tripping.
Top
#63034 - 03/04/06 08:39 PM Re: Underground fault
RODALCO Offline
Member
Registered: 12/08/05
Posts: 854
Loc: Titirangi, Akld, New Zealand
Megger cable first, 500 Vdc

Ph to Neutral.
Ph to Earth
Neutr to Earth
and from each individual core to ground, to establish if it's external damage

Have both ends disconnected,

Is it a screened cable?

or 2 or 3 core with no screen.

then fault locaion is easy.

POPIE for an earth fault or Thumper for internal cable fault.
_________________________
The product of rotation, excitation and flux produces electricty.
Top
#63035 - 03/05/06 01:47 AM Re: Underground fault
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
A TDR would also be handy.

A good one is pricy. But they jump through these kinds of challenges.
_________________________
Tesla
Top
#63036 - 03/05/06 01:49 PM Re: Underground fault
macmikeman Offline
Member
Registered: 07/16/02
Posts: 717
Loc: Honolulu, Hawaii
If this is under soil and not concrete, try this. Go to your nearest Big Orange store at about 7:00 am. Locate a couple of fellows hanging around the front area who dress and look like they are from outside your county line. I promise they will work at an affordable rate. Have them re-dig the thing and this time you can put in pvc and upgrade the whole shebang for the customer. Make sure though when you hire your new helpers, that you follow all state and federal hiring laws and also make sure that you have the proper workmans comp and other required insurance in place. This will probably be a less costly solution than trying to TDR the wire and locate a nick, unless you have ready access to the equipment.
Top
#63037 - 03/05/06 02:28 PM Re: Underground fault
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Mac..your profile says you're based in Hawaii. I've been to Hawaii; quite the cross-roads where Occident meets Orient.
Just what does "from across the county line" look like there?
Top
#63038 - 03/05/06 03:07 PM Re: Underground fault
mbhydro Offline
Member
Registered: 02/21/03
Posts: 347
Loc: Winnipeg MB Canada
Is Home Depot offering casual labour a new thing in the US?

Here where I am in Canada (Winnipeg MB) they don't do it. I can't even find service staff in the store (except at the checkout register) at that time of the morning.
Top
#63039 - 03/05/06 03:56 PM Re: Underground fault
macmikeman Offline
Member
Registered: 07/16/02
Posts: 717
Loc: Honolulu, Hawaii
Merly pointing out a time tested value packed way to get the fix in without resorting to a lot of test equippment and head scratching. Some days I can see across the county line from my window, but it is 27 miles across deep ocean so I can't quite see what they look like over there.
Top
#63040 - 03/05/06 04:29 PM Re: Underground fault
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
From what I understand picking up "casual labor" in London = finding a desperate American looking to work for the summer.
Guess it's the same world 'round?

Anyway back to the TOPIC....

Try the circuit (for testing purposes only) without the GFI and test for current.

No current.... Try a new GFI.

If all else fails, cut the power, grab the wire and aggressively rip it out of the ground. This will loosen the soil plenty for its replacement. (Without the casual labor)
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (ghost307), 67 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals