#63024 - 03/04/06 01:49 PM Bonding
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
I have a ongoing thing with my boss about bonding, we are doing a 450ft run of 4/0 and #2 ground. Going though 4 j-box's. There are no concentic k.o's all are punched, I say we should use bonding bushings not just locknuts for the bond. He says just plastic bushings. Who would be right. Thanks Sam

( This is a panel off the main gear )

[This message has been edited by Sparks30 (edited 03-04-2006).]
Top
Work Gear for Electricians and the Trades
#63025 - 03/04/06 02:55 PM Re: Bonding
bot540 Offline
Member
Registered: 09/14/04
Posts: 174
Loc: Vernon Hills, IL
While bonding bushings would not be a bad idea you don't need them. You only need them if using concentric or ecentric knockouts. Read 250.92 and 250.97
_________________________
Jesus may have been a capenter,but God was an electrician.Genesis1:3
Top
#63026 - 03/04/06 08:23 PM Re: Bonding
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
2005 NEC 250.92 is for services . As this is a feeder . (250.97) deals with Bonding over 250 volts to ground. If this was a 120/240 or 120/208 volt. Bonding bushings on a feeder would not be required Even if concentric or ecentric was involved. IF they were in good condition.
Top
#63027 - 03/04/06 08:46 PM Re: Bonding
bot540 Offline
Member
Registered: 09/14/04
Posts: 174
Loc: Vernon Hills, IL
Most inspectors around here(Northern Illinois) make you put them on with concentric or ecentric knockouts. Especially for feeders.
_________________________
Jesus may have been a capenter,but God was an electrician.Genesis1:3
Top
#63028 - 03/05/06 06:03 AM Re: Bonding
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
When the inspector looked at the underground branch he said he would be looking for the rigid sweeps and EMT to be grounded. Thanks for the input. Sam
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals