The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (ampherder), 233 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#62566 - 02/19/06 08:07 AM Need to learn fast about Mi cable Need to learn fast about Mi cable
jjmontey Offline
Junior Member

Registered: 05/01/04
Posts: 2
Loc: Mantua ,NJ,
I have a G.C. who is on my back about closing a shaft that has to have a mi cable installed. The mi cable is not going to get to the job site for another month. The print shows 3-#2 and a #8gnd M.I. I believe the #8 is a mistake because the copper sheathing will be the equipment ground. Can I sleeve the shaft with EMT or PVC? If I use EMT, do I have to bond the MI cable to the conduit? Is PVC permitted in the shaft? What size conduit should I use and can I have any bends for a 60-foot vertical run?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#62567 - 02/19/06 08:32 AM Re: Need to learn fast about Mi cable Need to learn fast about Mi cable
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
JJ:
Welcome to ECN.
READ Article 332 of '02 NEC (New Jersey)
You can 'fish' MI, and based on a quick read I did not notice any restrictions on putting it in a raceway

WATCH the bend radius, it's based on the OD, & you probably fall in the '9 times'. You need the OD to decide on conduit size. As to PVC, what is the rating of the 'shaft'

John
_________________________
John

Top
#62568 - 02/20/06 03:36 AM Re: Need to learn fast about Mi cable Need to learn fast about Mi cable
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
 Quote:
I believe the #8 is a mistake because the copper sheathing will be the equipment ground.


Is it possible the 8 AWG is actually a reduced neutral?
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top