The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 208 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#62537 - 02/17/06 06:03 PM Fire pump service disconnect
Jps1006 Offline
Member

Registered: 01/22/04
Posts: 609
Loc: Northern IL
If I have a 60HP 3-phase 208 motor with a RLA 140 amps and a LRC of 1000 amps, do I set a 200-amp service using 1000-amp equipment?

Anyone have any experience with these and can describe what your set-up looked like?

Thanks.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#62538 - 02/18/06 07:45 PM Re: Fire pump service disconnect
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
You'll be using 1200 Amp frame equipment.

Go to 695.4 B (1)
_________________________
Tesla

Top
#62539 - 02/20/06 08:55 AM Re: Fire pump service disconnect
Jps1006 Offline
Member

Registered: 01/22/04
Posts: 609
Loc: Northern IL
Tesla, why do you say 1200 amp? Do you interpret indefinatly to be continuous load? wouldn't that be no smaller than 1250-amp?

I don't know if it was in the specs or if I am recalling this from another site, but I thought the controller was set to only allow locked rotor current for 20 seconds.

Do you guys normally meter these? I have a meeting set up with the utility for sometime this week, so I'll find out what they want, but I'm curious what some have done in the past.

Top
#62540 - 02/23/06 07:07 PM Re: Fire pump service disconnect
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
2002 NEC handbook page 975-976 gives Example and explains it all.

Top