The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Ruben Rocha
01/18/17 07:05 PM
ESA Arc flash course
by frank
01/18/17 04:25 PM
Re: Fabricating Guards out of Lexan?
by frank
01/17/17 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
01/17/17 01:26 PM
Why cables look like they do
by Texas_Ranger
01/17/17 12:33 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 26
HotLine1 21
Ruben Rocha 14
Trumpy 12
ghost307 12
Who's Online
2 registered (Webmaster, Ruben Rocha), 0 Guests and 187 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#62337 - 02/14/06 10:21 PM 347 lighting
Cinner Offline
Member

Registered: 12/01/04
Posts: 77
Loc: Kelowna, B.C., Canada
Is it proper lockout procedure to shut off the other 2 phases sharing the neutral with thge circuit you are working on?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#62338 - 02/15/06 04:26 AM Re: 347 lighting
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
yes
_________________________
Don(resqcapt19)

Top
#62339 - 02/15/06 05:03 AM Re: 347 lighting
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
With power left on two other phases sharing the neutral, if you lifted that neutral at some point you could end up with voltage on one side via the loads.

Not only would this represent a shock-risk to you, it could also unbalance the voltages on those other loads. Given a large load on one phase and a small load on the other, you could see the voltage across the latter rise to almost the phase-to-phase level.

Top
#62340 - 02/15/06 06:16 PM Re: 347 lighting
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
You know, this is one thing NEVER mentioned in "lock-out' discussions. The same point also applies to single phase, multi-wire circuits- that is, where two 'legs' share a neutral!

I found this out the hard way...when a money changer was momentarily supplied with 220v...I really loved having to buy a $600 power supply (as part of a $100 add-a-receptacle job)!

An added clarification....if you are "downstream" of any point where the other circuits might be, then there is no need to isolate them as well. But if...as is often the cas...you have all phases present in the run of lights, they all ought to be killed.

[This message has been edited by renosteinke (edited 02-15-2006).]