The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 214 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#61988 - 02/07/06 04:38 PM Fittings for conduit repair
hypress Offline
Member

Registered: 07/20/04
Posts: 132
Loc: Charleston WV
During the late 70's and through 80's Chrouse Hinds made fittings for broken conduit repair. They had extremely fine threads to screw on the unthreaded conduit and on one end and standard threads male or female depending on the application. They were hex shaped so they could be threaded on with a crescent wrench. I have looked for these fittings for several years and not been able to find them. Does anyone know of such a fitting by anouther manufacturer. PS I think theywere approved for hazardous locations. Set screw / threadless fittings will not work for me THANKS HYPRESS

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#61989 - 02/07/06 05:14 PM Re: Fittings for conduit repair
Celtic Offline
Member

Registered: 02/26/05
Posts: 367
Loc: NJ
 Quote:
...They had extremely fine threads to screw on the unthreaded conduit ....Set screw / threadless fittings will not work...


HUH?
Fine threads?

What kind of pipe are you talking about?
342.28 ~ IMC
344.28 ~ RMC

Both state:
Where conduit is threaded in the field, a standard cutting die with a 1 in 16 taper (3/4-in. taper per foot) shall be used.


Don't get mixed up with pipe size/type and your threadless or compression fittings. For example, a 3/4" RMC will NOT accept a 3/4" EMT compression fitting....likewise, a 3/4" EMT will NOT accept a 3/4" threadless fitting.
Threadless and compression are two different animals.
_________________________
~~ CELTIC ~~
...-= NJ =-...

Top
#61990 - 02/07/06 06:02 PM Re: Fittings for conduit repair
hypress Offline
Member

Registered: 07/20/04
Posts: 132
Loc: Charleston WV
The fitting cut its own threads as it was screwed on. It is for repair work.

Top
#61991 - 02/07/06 06:17 PM Re: Fittings for conduit repair
Celtic Offline
Member

Registered: 02/26/05
Posts: 367
Loc: NJ
 Quote:
The fitting cut its own threads as it was screwed on.


Really?
 Quote:
Where conduit is threaded in the field, a standard cutting die with a 1 in 16 taper (3/4-in. taper per foot) shall be used.


I have never heard of a fitting that self threads a fine thread - that is not to say it never existed.

Contact CH and see what they have to say.
http://www.crouse-hinds.com/contact.cfm
_________________________
~~ CELTIC ~~
...-= NJ =-...

Top
#61992 - 02/07/06 10:15 PM Re: Fittings for conduit repair
venture Offline
Member

Registered: 01/08/06
Posts: 37
Loc: San Diego Ca USA
Appleton makes a repair union you describe For rigid conduit. I have used them often for repairs and they work good. Tip: oil the pipe often it is a workout threading it on. Rod

Top
#61993 - 02/08/06 03:31 AM Re: Fittings for conduit repair
tkb Offline
Member

Registered: 12/04/04
Posts: 94
Loc: Massachusetts
These are for rigid conduit.
I believe they are called "thread makers".
I have used them about 10 years ago.

Top
#61994 - 02/08/06 06:09 AM Re: Fittings for conduit repair
ghost307 Offline
Member

Registered: 05/09/05
Posts: 884
Loc: Chicago Illinois USA
I've recommended an Appleton product when confronted with this type of a situation and it always worked out well. They also make a setscrew version, but I'm not sold on the integrity of the ground path when the entire rest of the run consists of threaded fittings.
http://www.appletonelec.com/pdf/Threadless.pdf
_________________________
Ghost307

Top
#61995 - 02/08/06 09:16 AM Re: Fittings for conduit repair
walrus Offline
Member

Registered: 07/25/02
Posts: 671
Loc: Bangor Me. USA
I've repaired alot of broken 3/4 rigid by using a rigid pipe die from a hand threader, turning it with an offset pipe wrench. I've done it with wires in it, use a rat tail file to take any burrs out. It might not be the ideal solution but it worked

Top
#61996 - 02/08/06 10:48 AM Re: Fittings for conduit repair
ghost307 Offline
Member

Registered: 05/09/05
Posts: 884
Loc: Chicago Illinois USA
...or you could thread the ends like Walrus says and use one of these http://www.appletonelec.com/pdf/Bolt-On.pdf

You can take the bolt and spacer out and slide it (carefully, please) over the wires; then reassamemble the fitting and you're good to go.
_________________________
Ghost307

Top