#61984 - 02/07/06 03:19 PM Need a little help
scjohn Offline
Member
Registered: 07/04/02
Posts: 74
Loc: charleston, SC, USA
I have a foreign piece of equipment that is 3 phase 380 volt 23kw with a 60 amp start up and 45 amps running. This equipment came with a step-up or buck & boost transformer that is 30kva with a 3 phase 208 deta for primary and 400/231 y secondary. The problem I have is the building only has single phase 240volt power so I guess I need a phase converter. Is a 30kva converter enough, and what can I expect my load to be on the single phase circuit supplying all this? This piece of equipment is extremely vital and expensive, I don't want to screw it up.
Thanks.
Top
Work Gear for Electricians and the Trades
#61985 - 02/07/06 04:52 PM Re: Need a little help
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
If the converter is rated to supply 30kva, and the load requires 23kw, you're probably okay, but the difference between kW and kva, the ratio being the power factor, could overload the conveter.

The best bet is to contact the converter maker with the specific specifications (is that redundant?) of your equipment for proper application.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#61986 - 02/08/06 04:27 AM Re: Need a little help
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
scjohn, I did a search here on this site, and there was talk of derating phase convertors, up to 57%....

I have very limited experience with these, but will tell you, rotary convertors put out a high leg, and this should not be used for control circuits. If your equipment is "vital and expensive" as you say, then Larry's advise would be prudent. Contact both, the convertor manufacturer and the equipment manufacturer prior to installation.....


Dnk...
Top
#61987 - 02/08/06 07:15 PM Re: Need a little help
scjohn Offline
Member
Registered: 07/04/02
Posts: 74
Loc: charleston, SC, USA
Actually the step-up transformer that came with it states a 208 delta for a primary. This in itself is confusng me a little. I always thought that a delta was 240volt with a high leg, and 208y was 120volt from each line to ground. The secondary of the transformer is 400/235 y.
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 91 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals