#61889 - 02/04/06 03:11 PM Rough inspection without service panel?
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Has anyone had a residential rough wire inspection without the service panels installed? Are the panels necessary?
Top
Work Gear for Electricians and the Trades
#61890 - 02/04/06 03:17 PM Re: Rough inspection without service panel?
LoneGunman Offline
Member
Registered: 10/02/05
Posts: 141
Loc: Florida
Never heard of a rough without having the panels in. We didnt install breakers for the rough but all the wires were in the panel for it.
Top
#61891 - 02/04/06 03:27 PM Re: Rough inspection without service panel?
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6775
Loc: Brick, NJ USA
Redsy:
We do 'rough' wire, either with or without the service being installed.

John
_________________________
John
Top
#61892 - 02/04/06 03:42 PM Re: Rough inspection without service panel?
luckyshadow Offline
Member
Registered: 01/04/05
Posts: 305
Loc: Maryland USA
Yes, It can be done . Here you can have a rough wire inspection and not have service completed. You will not get the service released to the poco until it is completed and inspected. I have always had the service and rough in at the same time.
Top
#61893 - 02/04/06 04:18 PM Re: Rough inspection without service panel?
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Thanks,Guys!
I usually do the service first, or at the asme time, but circumstances interfere this time, and I want to send out a bill for the rough.

Hotline,

It is in Edgewater Park, near Willingboro.
I'm a little anxious about my first NJ inspection. You guys are supposedly pretty thorough, and I didn't want to overlook some thing stupid.
Top
#61894 - 02/05/06 10:56 AM Re: Rough inspection without service panel?
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
Redsy overlook something?

Not a chance....

Dnk..
Top
#61895 - 02/05/06 11:20 AM Re: Rough inspection without service panel?
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6775
Loc: Brick, NJ USA
Redsy:
Na, you won't do nothing stupid!
I don't know anyone down that way.
But...the UCC and NEC is statewide, so on that note you should be fine.

As I said, normally, rough wire can be done without the service, service can be done without rough, but you need a "load" to keep the POCO happy.

EC's in the twp that I work in usually do rough & service, unless it's $$$, or the siding isn't up.

John
_________________________
John
Top
#61896 - 02/06/06 01:26 PM Re: Rough inspection without service panel?
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
Here there are service inspections, rough inspections, and final inspections. No need for the panel to be installed for anything other than the service inspection.
Top
#61897 - 02/06/06 02:41 PM Re: Rough inspection without service panel?
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6775
Loc: Brick, NJ USA
Scott:
You can get a final without a panel????

HA! HA!
Just joking around; you opened the door, so....

John
_________________________
John
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals