#61747 - 02/02/06 12:41 AM isolated nuetral in main disconnect?  
Clydesdale  Offline
Member
Joined: Nov 2004
Posts: 138
i opened a panel today on one of the new houses our company had wired and noticed that someone had removed the jumper for the grounding bar to the neutral bar. the panel is a 200A main breaker. Is this safe to do? I made sure I put all the grounds on the side the grounding electrode conductor was terminated on and all the neutrals on the side the neutral was terminated on....

The reason I am asking is because one of my coworkers was shocked by the range wire's grounded conductor. I was reading 35VAC from nuetral to ground. All breakers were in the tripped position as I had only just installed them. The only breaker that was turned on was for the panel receptacle.

Also...I temporarily fed a pullchain off the panel receptacle breaker, and used the ground bar(isolated) as a neutral...now that I'm thinking about it sounds pretty hazardous. a 100W type A lamp was drawing about .6 Amps. just to see what would happen, i turned off the breaker, and re-installed the groundbar/nuetral jumper, and when I turned the breaker back on, the bulb was burning much brighter, and I read (off the top of my head) roughly .8 Amps of current that the bulb was drawing....

Any and all input please..thank you.


Work Gear for Electricians and the Trades

#61748 - 02/02/06 12:55 AM Re: isolated nuetral in main disconnect?  
bot540  Offline
Member
Joined: Sep 2004
Posts: 174
Vernon Hills, IL
You must install the main bonding jumper. Read article 250.24. Not having this installed could cause all sorts of problems (better explained in the handbook)


Jesus may have been a capenter,but God was an electrician.Genesis1:3

#61749 - 02/02/06 08:00 AM Re: isolated nuetral in main disconnect?  
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
Assuming that this is the main panel (and not a sub-panel) it is supposed to have the bond in place.

From the description, it does sound as though this is the case. Your temporary lamp was using the grounding bus as the return, inserting the resistance of the grounding system and earth between it and the xfmr neutral. That would account for both the dimmer light and your 35V reading.



Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.7502 MB (Peak: 0.8729 MB) Zlib enabled. Server Time: 2017-03-26 11:00:19 UTC