The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 196 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#61591 - 01/28/06 06:08 PM Holiday light package, 15 or 20-amp?
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
I'm thinking that if you're going to do it, might as well go 20-amp, but it seems that everyone else does 15.
Thoughts?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#61592 - 01/28/06 08:10 PM Re: Holiday light package, 15 or 20-amp?
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Do 20a, no reason not to. Those lights just seem to multiply every year. Use a quality receptacle.
_________________________
Greg Fretwell

Top
#61593 - 01/29/06 09:19 AM Re: Holiday light package, 15 or 20-amp?
Rewired Offline
Member

Registered: 01/01/06
Posts: 567
Loc: Hamilton, Ontario, Canada
Definately 20A... I have 2 20A circuits for mine and had them both maxed out at 80%..... Then they came out with LED lights! Ahh well

Top
#61594 - 01/29/06 12:09 PM Re: Holiday light package, 15 or 20-amp?
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
There's really no reason to not use a 20 amp circuit for x-mas lights on the outside of the house. The reason being, obviously, 4 more amps can be used than on a 15 amp circuit.

I did a real nice job last month where I ran (2) 20amp branch circuits (1 for each outside GFI receptacle location), and had them operating off of a single pole, double throw T-103 time clock beside the panel. The customer was very happy with the work I had done too, :-)

Top
#61595 - 01/29/06 03:28 PM Re: Holiday light package, 15 or 20-amp?
Rewired Offline
Member

Registered: 01/01/06
Posts: 567
Loc: Hamilton, Ontario, Canada
T-103-70 Intermatic?
DOUBLE pole SINGLE throw 120V clock motor ya mean?
Sorry, flashback to the days of workin behind the "counter" LOL

A.D

Top
#61596 - 01/29/06 05:42 PM Re: Holiday light package, 15 or 20-amp?
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
Yes, double pole, single throw. My bad. What the hell was I thinking?

Oh, and I'm becoming very familiar with some of the model numbers for a number of products I use. For 11 years with 1 contractor, I never had to do any paperwork - just the actual work. Now I'm with a new company and I have to write down a code number for nearly everything I use! It's actually a pretty good idea to know the numbers of products used because the guy at the supply house most of the time knows the number but has no idea what the product is used for. Not all of them, but some. Don't mean any disrespect to the counter guys here :-)

Top
#61597 - 01/29/06 06:35 PM Re: Holiday light package, 15 or 20-amp?
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
A little calrification...

"Holiday lighting package" in new home construction means installing an additionla receptacle in the INTERIOR of the home at each front window, all on the same, different circuit than the general purpose receptacles, and all controlled form the same switch.
Usually, the most that will be plugged in each will be a single, or possibly a triple decorative candle fixture at about 25-40 watts each lamp.

Top
#61598 - 01/30/06 02:42 PM Re: Holiday light package, 15 or 20-amp?
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
REdsy:
Had one of them in a McMansion about 2 months back....EC did it in 12, had about 4-5 circuits....sw in each room, sideways duplex tucked right at window sill; 1/2 switched.