The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Members: Non-Members: Did you know?
by Admin
Today at 02:34 PM
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 36
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
1 registered (Admin), 83 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#61529 - 01/26/06 06:23 PM current leakage
BigB Offline
Member
Registered: 03/31/04
Posts: 727
Loc: Tucson, AZ USA
Just came from an interesting service call. It was a halfway house for veterans that I have worked at before. They have a number of duplex units built in the 50's, no equipment grounds at any receptacles.

Anyway a resident complained of shocks received off the refrig. When I got there they described the shocks as a snap accompianied by a blue spark. They get them whenever they touch anything metal and also the phone and the thermostat. Well I told them it was static electricity, but I would check the fridge anyway.

Well when the fridge is running, it will light my non contact tester when held close to the cabinet. So I got my analog meter and checked from a part of the fridge that was not painted to the grounded gas line nearby. I got about 13 volts. Remember this fridge has no equipment ground with the old 2 wire system.

So now I am thinking, in addition to the static shocks, they could've gotten a real current shock off the fridge. Is the 13 volts excessive? As soon as the fridge shuts off it goes away. I told them, short of running a new circuit, the only thing to do is get a new fridge. I know if I put in a GFCI it will not hold.
I know the code requires refrigerators to be grounded, but if they can't pay for a new circuit, what else is there to do?
Top
Work Gear for Electricians and the Trades
#61530 - 01/26/06 08:33 PM Re: current leakage
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
You are seeing the real reason refrigerators trip GFCIs. You have a short inside the compressor. If it was grounded it would quietly arc and spark inside the can in a freon bath until it finally quits.
_________________________
Greg Fretwell
Top
#61531 - 01/26/06 11:32 PM Re: current leakage
Sixer Offline
Member
Registered: 08/08/05
Posts: 264
Loc: Canada
I've run into "hot fridges" many times. Once you ground the fridge, the casing will no longer be hot. Thanks for the explanation gfretwell....I've always wondered how a compressor can have a short and energize the casing, and yet when you ground it, it not only solves the problem but the breaker doesn't trip.
_________________________
Sixer

"Will it be cheaper if I drill the holes for you?"
Top