#6145 - 12/23/01 07:45 PM Tap Conductors
aphares Offline
Member
Registered: 12/17/01
Posts: 37
Loc: Indiana
In the 2002 NEC, There is now a definition in Article 240.2 of a tap conductor. Does this definition change the tap rule, or anyhting. Example: would you be able to set a trough out side a building or structure, install tapped conductors from there, and into six disconnects (rule), without a main?
Any thoughts.....Or am I just way off base?
Top
Work Gear for Electricians and the Trades
#6146 - 12/23/01 08:00 PM Re: Tap Conductors
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
The definition was in 240-3(e) in the '99 code. There is no change in the application of the tap rules. The conductors in your example are not taps per the definition as they are service conductors. I see no problem with your example as long as the conductors leaving the trough have an ampacity at least equal to the OCPD installed in the disconnect. Of course the six disconencts would have to be grouped and nearset the point of entrance of the conductors.
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 41 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals